I am sorry, but I only have line-interactive ones.
But I did some research on the Eaton Website. These are the current models:
Online: Eaton 9130 Eaton EX Eaton 9SX Eaton 9PX Eaton 93PS Eaton BladeUPS Eaton 93E EATON 93PM Power Xpert 9395P
Line-interactive: Eaton 5S Eaton Ellipse PRO Eaton 5SC Eaton 5P Eaton 5130 Eaton 5PX
And these are only the current models, not to mention the MGE UPS ☺ So I guess it would be quite difficult to match on the FamilyName.
These are my two active UPS: MG-SNMP-UPS-MIB::upsmgIdentFamilyName.0 = STRING: "Evolution" MG-SNMP-UPS-MIB::upsmgIdentModelName.0 = STRING: "S 2500" MG-SNMP-UPS-MIB::upsmgOutputPhaseNum.0 = INTEGER: 1 MG-SNMP-UPS-MIB::upsmgOutputInverterOff.0 = INTEGER: yes(1)
MG-SNMP-UPS-MIB::upsmgIdentFamilyName.0 = STRING: "Eaton 5PX" MG-SNMP-UPS-MIB::upsmgIdentModelName.0 = STRING: "2200" MG-SNMP-UPS-MIB::upsmgOutputPhaseNum.0 = INTEGER: 1 MG-SNMP-UPS-MIB::upsmgOutputInverterOff.0 = INTEGER: yes(1)
Maybe this could be a useful OID: upsmgConfigByPassType (only online UPS have an internal static bypass) My two line-interactive are not returning anything if I walk this OID, maybe online UPS do?
Von: observium [mailto:observium-bounces@observium.org] Im Auftrag von Mike Stupalov Gesendet: Donnerstag, 04. August 2016 13:15 An: observium@observium.org Betreff: Re: [Observium] Eaton 5130 'Inverter Off' Flipped
Pls someone show .1.3.6.1.4.1.705.1.1.1.0 (upsmgIdentFamilyName.0) for online UPSes
On 04.08.16 13:04, Gumilar Siegfried wrote: I think I found something you could use to detect it. You could check OID 1.3.6.1.4.1.705.1.7.1 (upsmgOutputPhaseNum)
My guess is that UPS with only one phase are line-interactive and UPS with three phases are online. Correct me if I am wrong or that is not always applicable.
Von: observium [mailto:observium-bounces@observium.org] Im Auftrag von Mike Stupalov Gesendet: Donnerstag, 04. August 2016 11:50 An: observium@observium.orgmailto:observium@observium.org Betreff: Re: [Observium] Eaton 5130 'Inverter Off' Flipped
Hi,
confusion between MGE/Eaton, because Eaton acquired MGE in 2007 year.
About "Inverter Off" sensor - I walked multiple such devices, and confirm I see on some devices it set as "yes", on some as "no". But I not see any param/way for detect if ups line-interactive or online (by snmp). If someone know - show me.
On 04.08.16 11:32, Robert Williams wrote: Ahhh… yes that makes perfect sense thanks!
So yes the question now becomes – is there a way to set this in Observium?
Doing it by model would be painful, maybe you could set the state during a discovery to be the ‘good’ state? As the chances of a power fail being present at the exact moment of discovery are relatively small…
Robert Williams Custodian Data Centre Email: Robert@CustodianDC.commailto:Robert@CustodianDC.com http://www.CustodianDC.com From: observium [mailto:observium-bounces@observium.org] On Behalf Of Gumilar Siegfried Sent: 04 August 2016 09:21 To: Observium Network Observation System observium@observium.orgmailto:observium@observium.org Subject: Re: [Observium] Eaton 5130 'Inverter Off' Flipped
Hi,
we are using some MGE UPS that are similar to your Eaton UPS and we have the same issue.
I recently talked to an Eaton Engineer and he explained to me that our UPS are line-interactive and therefore the inverter has to be off in normal operation. For the bigger “online UPS” on the other hand the inverter has to be on.
It seems like Observium is configured to treat all the Eaton and MGE UPS as online UPS. Maybe there is a way for Observium to detect whether it is an online or line-interactive UPS and handle the inverter Alert accordingly.
Regards, Siegfried
Von: observium [mailto:observium-bounces@observium.org] Im Auftrag von Robert Williams Gesendet: Donnerstag, 04. August 2016 09:58 An: Observium Network Observation System (observium@observium.orgmailto:observium@observium.org) Betreff: [Observium] Eaton 5130 'Inverter Off' Flipped
Hi,
We’ve got several Eaton 5130 RT 3000 (with extended battery packs) being deployed to some remote locations. One of my guys has been setting them up overnight but has noticed that Observium reports one of the metrics incorrectly for all of the new units.
Ironically the inverter status is, well, inverted.
[cid:image001.jpg@01D1EE53.CDB3E470]
The platform is detected as:
Hardware 5130 RT 3000 Operating system MGE UPS 6006AC (Firmware: JI)
A debug of the status module, shows:
SQL[UPDATE `status-state` set `status_value` ='2',`status_name` ='No',`status_event` ='ok',`status_last_change` ='1470278633',`status_polled` ='1470295701' WHERE `status_id` = '1289'] SQL RUNTIME[0.00013590s] Checking (snmp) Inverter Off
CMD[/usr/bin/snmpget -v1 -c *** -Pu -OUqnv -m SNMPv2-MIB -M /opt/observium/mibs/rfc:/opt/observium/mibs/net-snmp 'udp':'ups-41.thn.oob.local':'161' .1.3.6.1.4.1.705.1.7.9.0]
CMD EXITCODE[0] CMD RUNTIME[0.0414s] STDOUT[ 1 ] SNMP STATUS[TRUE]
RRD CMD[update /opt/observium/rrd/ups-41.thn.oob.local/status-mge-status-state-upsmgOutputInverterOff.1.0.rrd N:1 --daemon unix:/var/run/rrdcached.sock] RRD RUNTIME[0.0011s] RRD STDOUT[OK u:0.00 s:0.00 r:0.65] RRD_STATUS[TRUE]
- /opt/observium/includes/polling/status.inc.php:45 /opt/observium/includes/alerts.inc.php:61 ================================================ array( [status_value] => int(1) [status_name] => string(3) "Yes" [status_name_uptime] => int(17068) [status_event] => string(5) "alert" ))
Reading the standards for that OID, that does seem to be the wrong way around.
After a simulated power failure, you can see it goes to ‘2’ when the power is failed and the inverter is (actually) off.
[cid:image002.jpg@01D1EE53.CDB3E470]
As a side note, I noticed that Observium is polling the OIDs for a Merlin Gerin unit (.1.3.6.1.4.1.705.x) for when the unit is actually Eaton.
Should it maybe be looking here instead?
iso.3.6.1.4.1.534.1.1.1.0 = STRING: "EATON" iso.3.6.1.4.1.534.1.1.2.0 = STRING: "5130 RT 3000" iso.3.6.1.4.1.534.1.1.3.0 = STRING: "INV: 6006AC" iso.3.6.1.4.1.534.1.1.4.0 = INTEGER: 0 iso.3.6.1.4.1.534.1.2.1.0 = INTEGER: 350 iso.3.6.1.4.1.534.1.2.2.0 = INTEGER: 78 iso.3.6.1.4.1.534.1.2.3.0 = INTEGER: 0 iso.3.6.1.4.1.534.1.2.4.0 = INTEGER: 23 iso.3.6.1.4.1.534.1.2.5.0 = INTEGER: 1 iso.3.6.1.4.1.534.1.2.6.0 = "" iso.3.6.1.4.1.534.1.3.1.0 = INTEGER: 490 iso.3.6.1.4.1.534.1.3.2.0 = Counter32: 0 iso.3.6.1.4.1.534.1.3.3.0 = INTEGER: 1 iso.3.6.1.4.1.534.1.3.4.1.1.1 = INTEGER: 1 iso.3.6.1.4.1.534.1.3.4.1.2.1 = INTEGER: 226 iso.3.6.1.4.1.534.1.3.4.1.3.1 = INTEGER: 0 iso.3.6.1.4.1.534.1.3.4.1.4.1 = INTEGER: 0 iso.3.6.1.4.1.534.1.3.4.1.5.1 = INTEGER: 1 iso.3.6.1.4.1.534.1.3.5.0 = INTEGER: 3 iso.3.6.1.4.1.534.1.4.1.0 = INTEGER: 67 iso.3.6.1.4.1.534.1.4.2.0 = INTEGER: 490 iso.3.6.1.4.1.534.1.4.3.0 = INTEGER: 1 iso.3.6.1.4.1.534.1.4.4.1.1.1 = INTEGER: 1 iso.3.6.1.4.1.534.1.4.4.1.2.1 = INTEGER: 226 iso.3.6.1.4.1.534.1.4.4.1.3.1 = INTEGER: 8 iso.3.6.1.4.1.534.1.4.4.1.4.1 = INTEGER: 1809 iso.3.6.1.4.1.534.1.4.4.1.5.1 = INTEGER: 1 iso.3.6.1.4.1.534.1.4.5.0 = INTEGER: 3 iso.3.6.1.4.1.534.1.4.6.0 = INTEGER: 0 iso.3.6.1.4.1.534.1.4.7.0 = INTEGER: 0 iso.3.6.1.4.1.534.1.4.8.0 = Counter32: 0 iso.3.6.1.4.1.534.1.5.1.0 = INTEGER: 0 iso.3.6.1.4.1.534.1.5.2.0 = INTEGER: 0 iso.3.6.1.4.1.534.1.6.1.0 = INTEGER: 0 iso.3.6.1.4.1.534.1.6.2.0 = INTEGER: 0 iso.3.6.1.4.1.534.1.6.3.0 = INTEGER: 40 iso.3.6.1.4.1.534.1.6.7.0 = INTEGER: 0 iso.3.6.1.4.1.534.1.7.1.0 = Gauge32: 0 iso.3.6.1.4.1.534.1.7.18.0 = Gauge32: 0 iso.3.6.1.4.1.534.1.8.1.0 = INTEGER: 1 iso.3.6.1.4.1.534.1.8.2.0 = INTEGER: 2 iso.3.6.1.4.1.534.1.9.1.0 = INTEGER: 0 iso.3.6.1.4.1.534.1.9.2.0 = INTEGER: 0 iso.3.6.1.4.1.534.1.9.3.0 = INTEGER: 0 iso.3.6.1.4.1.534.1.9.4.0 = INTEGER: 0 iso.3.6.1.4.1.534.1.9.5.0 = INTEGER: 0 iso.3.6.1.4.1.534.1.9.6.0 = INTEGER: 0 iso.3.6.1.4.1.534.1.9.7.0 = INTEGER: 0 iso.3.6.1.4.1.534.1.10.1.0 = INTEGER: 230 iso.3.6.1.4.1.534.1.10.2.0 = INTEGER: 230 iso.3.6.1.4.1.534.1.10.3.0 = INTEGER: 2700 iso.3.6.1.4.1.534.1.10.4.0 = INTEGER: 500 iso.3.6.1.4.1.534.1.10.5.0 = STRING: "08/04/2016 08:34:38" iso.3.6.1.4.1.534.1.10.6.0 = INTEGER: 160 iso.3.6.1.4.1.534.1.10.7.0 = INTEGER: 294 iso.3.6.1.4.1.534.1.10.8.0 = "" iso.3.6.1.4.1.534.1.11.1.0 = INTEGER: 5 iso.3.6.1.4.1.534.1.11.2.0 = INTEGER: 2 iso.3.6.1.4.1.534.1.11.3.0 = "" iso.3.6.1.4.1.534.1.12.1.0 = INTEGER: 2 iso.3.6.1.4.1.534.1.12.2.1.1.1 = INTEGER: 1 iso.3.6.1.4.1.534.1.12.2.1.1.2 = INTEGER: 2 iso.3.6.1.4.1.534.1.12.2.1.2.1 = INTEGER: 1 iso.3.6.1.4.1.534.1.12.2.1.2.2 = INTEGER: 1 iso.3.6.1.4.1.534.1.12.2.1.3.1 = INTEGER: -1 iso.3.6.1.4.1.534.1.12.2.1.3.2 = INTEGER: -1 iso.3.6.1.4.1.534.1.12.2.1.4.1 = INTEGER: -1 iso.3.6.1.4.1.534.1.12.2.1.4.2 = INTEGER: -1 iso.3.6.1.4.1.534.1.12.2.1.5.1 = INTEGER: -1 iso.3.6.1.4.1.534.1.12.2.1.5.2 = INTEGER: -1 iso.3.6.1.4.1.534.1.12.2.1.6.1 = INTEGER: 3 iso.3.6.1.4.1.534.1.12.2.1.6.2 = INTEGER: 6 iso.3.6.1.4.1.534.1.12.2.1.7.1 = INTEGER: 0 iso.3.6.1.4.1.534.1.12.2.1.7.2 = INTEGER: 0 iso.3.6.1.4.1.534.1.12.2.1.8.1 = INTEGER: 0 iso.3.6.1.4.1.534.1.12.2.1.8.2 = INTEGER: 0 iso.3.6.1.4.1.534.1.12.2.1.9.1 = INTEGER: 0 iso.3.6.1.4.1.534.1.12.2.1.9.2 = INTEGER: 0 iso.3.6.1.4.1.534.1.12.2.1.10.1 = Counter32: 0 iso.3.6.1.4.1.534.1.12.2.1.10.2 = Counter32: 0 iso.3.6.1.4.1.534.1.13.1.0 = INTEGER: 32 iso.3.6.1.4.1.534.1.13.2.0 = INTEGER: 0 iso.3.6.1.4.1.534.1.13.3.0 = INTEGER: 0
I could be very wrong, maybe there is a valid reason to us the Merlin Gerin instead (I know they merged, but I thought I’d mention it in light of the odd issue).
Any ideas anyone? Cheers!
Robert Williams Custodian Data Centre Email: Robert@CustodianDC.commailto:Robert@CustodianDC.com http://www.CustodianDC.com
_______________________________________________
observium mailing list
observium@observium.orgmailto:observium@observium.org
http://postman.memetic.org/cgi-bin/mailman/listinfo/observium
--
Mike Stupalov
_______________________________________________
observium mailing list
observium@observium.orgmailto:observium@observium.org
http://postman.memetic.org/cgi-bin/mailman/listinfo/observium
--
Mike Stupalov