
Hi Mike – thanks very much for that, confirmed working in 8326.
Cheers!
From: observium [mailto:observium-bounces@observium.org] On Behalf Of Mike Stupalov Sent: 17 January 2017 23:15 To: Observium Network Observation System observium@observium.org Subject: Re: [Observium] UPS Input Current Detection
Hi, try with r8326, both issues should be fixed.
On Tue, Jan 17, 2017 at 7:13 PM, Robert Williams <Robert@custodiandc.commailto:Robert@custodiandc.com> wrote: Hi,
Ok, they are all in “ups-mib” it seems.
Interestingly someone must have done a hardcoded override for detection of the “Bypass Current” sensors because they _always_ appear in the list but are always zero.
[cid:image001.png@01D2715D.9789BF90]
(The missing sensor on screenshot above was upsInputEntry.1 )
Since Input Current is (should be) always a working valid primary sensor, I believe it should be hardcoded to appear even when zero. In my opinion it is >= the validity of the already hardcoded Bypass Current sensor. FWIW - I can see why the bypass was hardcoded, because in most cases that is actually zero, but you still want to have it because when it goes active you know you have an issue and you want to set thresholds on it in most cases.
Short version – can we hard-code Input Current to show up in the same manner as (I guess) Bypass Current is?
Cheers! :)
Robert Williams Custodian Data Centre Email: Robert@CustodianDC.commailto:Robert@CustodianDC.com http://www.CustodianDC.com
Robert Williams Custodian Data Centre Email: Robert@CustodianDC.com http://www.CustodianDC.com From: observium [mailto:observium-bounces@observium.orgmailto:observium-bounces@observium.org] On Behalf Of Adam Armstrong Sent: 17 January 2017 01:10 To: observium@observium.orgmailto:observium@observium.org Subject: Re: [Observium] UPS Input Current Detection
Hi,
This is probably them being ignored by discovery when the value is zero, because often these devices have lots of missing sensors whos value is always zero.
It's difficult to know without knowing exactly what these sensors are and which module they came from (device -> settings -> sensors should have that info)
adam.
On 16/01/2017 09:41:53, Robert Williams <robert@custodiandc.commailto:robert@custodiandc.com> wrote: Hi,
Got a weird issue with UPS data collection for devices that are in ‘Eco Mode’. (I’m not a fan of the mode, but some customers run them this way.)
In brief, it means the UPS is running on internal bypass with the inverter synchronised but off-load. When there is a failure then it starts being a UPS again, quickly. This means that 99.9% of the time it has near-zero “Input Current” because the load is being fed from the bypass line. This seems to cause Observium to cease polling the values for the Input Currents (they are zero, or near-zero) on some of the three phases.
The most annoying side effect is that they disappear and re-appear (depending if the value is zero or 0.1A) during each detection run, so the custom sensor values seem to get reset. Causing random alarms when the values drop to zero again.
Interestingly, it does not seem to have this issue with the Bypass Current which (in this device) isn’t metered and therefore is always zero, but always gets found OK.
There is residual current on Input Phase 2 and Input Phase 3 but rarely does it show anything on Input Phase 1 (until the UPS goes active).
I hope that this all makes a small amount of sense - attached is a debug discovery and a debug poll of the sensors module for this example device. (The last run I did it found Phase 2 and Phase 3.)
I have also attached an SNMP walk of the device. I’ve done this several times and I always get all the OIDs responded to, but phases 1 and 2 are often zero:
root@:~# snmpwalk <blah> 1.3.6.1.2.1.33.1.3.3.1.4 iso.3.6.1.2.1.33.1.3.3.1.4.1 = INTEGER: 0 iso.3.6.1.2.1.33.1.3.3.1.4.2 = INTEGER: 1 iso.3.6.1.2.1.33.1.3.3.1.4.3 = INTEGER: 2 root@:~# snmpwalk <blah> 1.3.6.1.2.1.33.1.3.3.1.4 iso.3.6.1.2.1.33.1.3.3.1.4.1 = INTEGER: 0 iso.3.6.1.2.1.33.1.3.3.1.4.2 = INTEGER: 1 iso.3.6.1.2.1.33.1.3.3.1.4.3 = INTEGER: 2 root@:~# snmpwalk <blah> 1.3.6.1.2.1.33.1.3.3.1.4 iso.3.6.1.2.1.33.1.3.3.1.4.1 = INTEGER: 0 iso.3.6.1.2.1.33.1.3.3.1.4.2 = INTEGER: 1 iso.3.6.1.2.1.33.1.3.3.1.4.3 = INTEGER: 2 root@:~# snmpwalk <blah> 1.3.6.1.2.1.33.1.3.3.1.4 iso.3.6.1.2.1.33.1.3.3.1.4.1 = INTEGER: 0 iso.3.6.1.2.1.33.1.3.3.1.4.2 = INTEGER: 0 iso.3.6.1.2.1.33.1.3.3.1.4.3 = INTEGER: 1 root@:~# snmpwalk <blah> 1.3.6.1.2.1.33.1.3.3.1.4 iso.3.6.1.2.1.33.1.3.3.1.4.1 = INTEGER: 0 iso.3.6.1.2.1.33.1.3.3.1.4.2 = INTEGER: 0 iso.3.6.1.2.1.33.1.3.3.1.4.3 = INTEGER: 1
So – bug or UPS card fail? Any ideas? Cheers!
Robert Williams Custodian Data Centre Email: Robert@CustodianDC.commailto:Robert@CustodianDC.com http://www.CustodianDC.com
_______________________________________________ observium mailing list observium@observium.orgmailto:observium@observium.org http://postman.memetic.org/cgi-bin/mailman/listinfo/observium
-- Mike Stupalov http://observium.org/