I'd just alert on "status_event notequals up" to catch all fail states, unless you really want separate checkers/contacts depending on what's wrong with the thing :)
On 2016-02-08 15:05, Moerman, Maarten wrote:
You can alert when the value does not equal 2 (from the looks of it)
Maarten
Maarten Moerman | Mgr, Network Engineering | eBay Classifieds | +31-655122247 | mmoerman@ebay.com
From: observium on behalf of Spencer Ryan Reply-To: Observium Network Observation System Date: Monday, February 8, 2016 at 3:03 PM To: Observium Network Observation System Subject: [Observium] Alert check config for a UPS "Status" entry
We'd like to alert when any of our APC UPS'es output status is not "online"
I see an alert check type is "status" but I'm not sure what to use for the other settings.
Right now we have a UPS in hardware bypass due to a bad inverter (ugh) and the status entry says "event alert, status hardwareFailureBypass".
Any tips?
Spencer Ryan* | Senior Systems Administrator | sryan@arbor.net mailto:sryan@arbor.net *Arbor Networks* +1.734.794.5033 (d) | +1.734.846.2053 (m) www.arbornetworks.com http://www.arbornetworks.com/