Hi,
thx, this worked!
Regards,
Christian
Von: observium [mailto:observium-bounces@observium.org]
Im Auftrag von Simon Smith
Gesendet: Donnerstag, 22. Mai 2014 16:00
An: Observium Network Observation System
Betreff: Re: [Observium] Mikrotik RouterOS 6 Sensors
Hi,
you can go into the settings in the device on Observium and set custom values…
this is what i had to do with our Mikrotik switches i monitor
Devices -> select device -> Settings Icon -> Sensors
Then set your High and Low values here
Also make sure Custom Limits is set to YES
then save :-)
Hope this helps
Regards
Simon
On 22 May 2014, at 14:55, Christian Mladek <c.mladek@hotze.com> wrote:
Hy observium-users,
we’re using observium with many devices and all sensors report a correct state.
But with Mikrotik RB2011 we’re getting temperature and voltage warnings from „System 0“.
The reported values seem ok, but the thresholds are wrong.
e.g. temperature 0C – 5.6C, voltage 1.04V – 1.4V
how can we fix this behaviour?
screens attached: