Hello
The device is a gateway for the modbus connected devices. Reading the official modbus faq about such setups it states:
"Since Modbus TCP/IP is simply Modbus protocol with a TCP wrapper, it is very simple for existing Modbus devices to communicate over Modbus TCP/IP. A gateway device is required to convert from the current physical layer (RS232, RS485 or others) to Ethernet and to convert Modbus protocol to Modbus TCP/IP. Such a gateway device could be implemented using a PC. Commercial products to do this are available from several different manufactures. The Modbus device database can help you identify gateways and other Modbus devices."
So yes, I'd say you're correct that you'd need to speak Modbus TCP/IP to actually understand the slave device connected to the gateway.
Here's a snmpwalk of the gateway: http://pastebin.com/TbiZT8zn
And observium does not speak Modbus TCP, right?
Cheers and thanks
-- Henrik Cednert cto | td | compositor
Filmlance International Direct + 46 (0)704 71 89 54
On 21/01/16 00:16, "observium on behalf of Michael Loftis" <observium-bounces@observium.org on behalf of mloftis@wgops.com> wrote:
I don't see any technical documentation readily visible there, and from the basic description SNMP is not for polling the Modbus but ONLY for monitoring the TSXETG100 itself. You have to speak Modbus/TCP to speak to the device(s) behind.
On Fri, Jan 15, 2016 at 2:39 PM, Henrik Cednert (Filmlance) henrik.cednert@filmlance.se wrote:
Hi
I have a schneider tsxetg100 ethernet gateway that has a PowerLogic PM3250 attached to it. I can successfully monitor this in APC StruxureWare Data Center expert but trying to get away from that solution. Observium does find and see the tsxetg100 as a generic device but I don't see the PowerLogic attached to it.
Is it possible to monitor a Modbus TCP device like this through the SNMP gateway?
The tsxetg100: http://www.schneider-electric.com/download/ww/en/details/25779671-TSXETG100-...
The Powerlogic: http://www.schneider-electric.com/en/product-range/61274-powerlogic-pm3000-s...
Cheers and thanks
-- Henrik Cednert cto | td | compositor
Filmlance International Direct + 46 (0)704 71 89 54
observium mailing list observium@observium.org http://postman.memetic.org/cgi-bin/mailman/listinfo/observium
--
"Genius might be described as a supreme capacity for getting its possessors into trouble of all kinds." -- Samuel Butler _______________________________________________ observium mailing list observium@observium.org http://postman.memetic.org/cgi-bin/mailman/listinfo/observium