Just updated to 6.9274, and still seeing the behavior on the following 2 entries... /opt/observium/includes/polling/functions.inc.php:72 array( [sensor_id] => string(6) "149562" [sensor_deleted] => string(1) "0" [sensor_class] => string(7) "current" [device_id] => string(2) "95" [poller_type] => string(4) "snmp" [sensor_oid] => string(33) ".1.3.6.1.4.1.318.1.1.26.6.3.1.5.1" [sensor_mib] => null [sensor_object] => null [sensor_index] => string(25) "rPDU2PhaseStatusCurrent.1" [sensor_type] => string(3) "apc" [sensor_descr] => string(12) "Unit 1 Ouput" [sensor_unit] => null [sensor_multiplier] => string(3) "0.1" [sensor_limit] => string(3) "1.2" [sensor_limit_warn] => string(3) "1.1" [sensor_limit_low] => null
AND... /opt/observium/includes/polling/functions.inc.php:72 array( [sensor_id] => string(6) "149565" [sensor_deleted] => string(1) "0" [sensor_class] => string(7) "current" [device_id] => string(2) "95" [poller_type] => string(4) "snmp" [sensor_oid] => string(33) ".1.3.6.1.4.1.318.1.1.26.6.3.1.5.2" [sensor_mib] => null [sensor_object] => null [sensor_index] => string(25) "rPDU2PhaseStatusCurrent.2" [sensor_type] => string(3) "apc" [sensor_descr] => string(12) "Unit 2 Ouput" [sensor_unit] => null [sensor_multiplier] => string(3) "0.1" [sensor_limit] => string(3) "1.2" [sensor_limit_warn] => string(3) "1.1" [sensor_limit_low] => null
derek
-----Original Message----- Sent: Wednesday, June 20, 2018 3:38 PM To: Observium observium@observium.org Subject: RE: [Observium] APC PDU values
Thanks, the rPDU2BankStatusCurrent.1 entries are now correct...but
rPDU2PhaseStatusCurrent.1 rPDU2PhaseStatusCurrent.2
are still off by a factor of 10.
derek
-----Original Message----- From: observium [mailto:observium-bounces@observium.org] On Behalf Of Adam Armstrong Sent: Wednesday, June 20, 2018 3:07 PM To: Observium observium@observium.org Subject: Re: [Observium] APC PDU values
Ahh. The thresholds are returned in amps, but the measurement is in deciamps. It seems we were expecting both to be in deciamps and were applying a 0.1 multiplier.
This is now fixed in revision 9270.
adam.
On 2018-06-20 14:34, Pedrosi, Derek G. wrote:
Not sure when this started (2 weeks ago?), but my APC PDUs (model AP8641) are alerting sensors on several banks.
I checked the output values on the PDU and they are correctly reported BOTH on the PDU and in Observium.
The issue lies at what Observium thinks the thresholds should be set to. On the PDU the thresholds are correct (16 warn and 20 max).
But Observium is reporting the thresholds as 1.6 and 2
Doing a discovery debug on the device I see this…
I feel that the SCALE value is being wrongly applied to several of the values, namely:
rPDU2BankStatusCurrent.1
rPDU2BankStatusCurrent.2
rPDU2BankStatusCurrent.3
rPDU2BankStatusCurrent.4
rPDU2PhaseStatusCurrent.1
rPDU2PhaseStatusCurrent.2
Regards,
derek _______________________________________________ observium mailing list observium@observium.org http://postman.memetic.org/cgi-bin/mailman/listinfo/observium
_______________________________________________ observium mailing list observium@observium.org http://postman.memetic.org/cgi-bin/mailman/listinfo/observium