Not sure when this started (2 weeks ago?), but my APC PDUs (model AP8641) are alerting sensors on several banks.
I checked the output values on the PDU and they are correctly reported BOTH on the PDU and in Observium.
The issue lies at what Observium thinks the thresholds should be set to. On the PDU the thresholds are correct (16 warn and 20 max).
But Observium is reporting the thresholds as 1.6 and 2
Doing a discovery debug on the device I see this…
I feel that the SCALE value is being wrongly applied to several of the values, namely:
rPDU2BankStatusCurrent.1
rPDU2BankStatusCurrent.2
rPDU2BankStatusCurrent.3
rPDU2BankStatusCurrent.4
rPDU2PhaseStatusCurrent.1
rPDU2PhaseStatusCurrent.2
Regards,
derek