23 May
2019
23 May
'19
4:11 a.m.
Hi,
thanks for reporting.
Load sensor scale fixed in r9912, need rediscovery device after update.
Laszlo Nemeth via observium wrote on 22/05/2019 15:48:
Hello,
I am happy that the Observium can monitoring the our HP PDUs too!
But i found a cosmetic problem.
Here is what the PDU shows:
And what the Observium (9906) shows me:
So the "Total Load Feed" looks like need to divide by 10.
If the mouse is over the "Power" green value (that is now 2.59kW) the popup shows me: "Normal state 64.31685344686dBm"
There is any option to shows the segments too not just the summarized power feed ? (like Load Segment 1..6)
Thanks
Laszlo
observium mailing list observium@observium.org http://postman.memetic.org/cgi-bin/mailman/listinfo/observium
--
Mike Stupalov
Observium Limited, http://observium.org