Hi Sweden!
These are the points from the Belgian vote:
You have issues with your monitored machines and would best fix them; your SNMP is timing out.
The agent df data is not used in Observium; so concentrate on the snmp values for hrStorage.
The fact that they disappeared 3 months ago and you didn't notice probably tells me they're not very important though ;)
Tom
On 10/07/2013 12:33 PM, Niklas Larsson wrote:
Hi,
after som updates (now on the latest public SVN) I have lost temperatures on my SuperMicro boxes. And on some the storage as well.
Log from ./discovery.php -d -h box01.example.com: https://gist.github.com/pnlarsson/2d207c05a47cc4de1361
Temperatures/Voltages/Fans:
They all went to 0 around 2013-07-10 (Voltage -12V above threshold: 0 V (> -10.729 V)). And deleted 2013-08-25 (Sensor Deleted: voltage supermicro 9 CPU1 Vcore).
I can get the temperatures/voltage/fans from cli with sd2 and from smtp with:
[root@observium observium]# snmpwalk -v2c -c 'SuperDuperPassword' box01.example.com .1.3.6.1.4.1.10876 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.2.1 = STRING: "Fan1 Fan Speed" SNMPv2-SMI::enterprises.10876.2.1.1.1.1.2.2 = STRING: "Fan2 Fan Speed" SNMPv2-SMI::enterprises.10876.2.1.1.1.1.2.3 = STRING: "Fan3 Fan Speed" SNMPv2-SMI::enterprises.10876.2.1.1.1.1.2.4 = STRING: "Fan4 Fan Speed" SNMPv2-SMI::enterprises.10876.2.1.1.1.1.2.5 = STRING: "Fan5 Fan Speed" SNMPv2-SMI::enterprises.10876.2.1.1.1.1.2.6 = STRING: "Fan6 Fan Speed" SNMPv2-SMI::enterprises.10876.2.1.1.1.1.2.7 = STRING: "Fan7 Fan Speed" SNMPv2-SMI::enterprises.10876.2.1.1.1.1.2.8 = STRING: "Fan8 Fan Speed" SNMPv2-SMI::enterprises.10876.2.1.1.1.1.2.9 = STRING: "CPU1 Vcore Voltage" SNMPv2-SMI::enterprises.10876.2.1.1.1.1.2.10 = STRING: "CPU2 Vcore Voltage" SNMPv2-SMI::enterprises.10876.2.1.1.1.1.2.11 = STRING: "CPU1 DIMM Voltage" SNMPv2-SMI::enterprises.10876.2.1.1.1.1.2.12 = STRING: "CPU2 DIMM Voltage" SNMPv2-SMI::enterprises.10876.2.1.1.1.1.2.13 = STRING: "+5V Voltage" SNMPv2-SMI::enterprises.10876.2.1.1.1.1.2.14 = STRING: "+5VSB Voltage" SNMPv2-SMI::enterprises.10876.2.1.1.1.1.2.15 = STRING: "+12V Voltage" SNMPv2-SMI::enterprises.10876.2.1.1.1.1.2.16 = STRING: "-12V Voltage" SNMPv2-SMI::enterprises.10876.2.1.1.1.1.2.17 = STRING: "+3.3V Voltage" SNMPv2-SMI::enterprises.10876.2.1.1.1.1.2.18 = STRING: "+3.3Vsb Voltage" SNMPv2-SMI::enterprises.10876.2.1.1.1.1.2.19 = STRING: "VBAT Voltage" SNMPv2-SMI::enterprises.10876.2.1.1.1.1.2.20 = STRING: "CPU1 Temperature" SNMPv2-SMI::enterprises.10876.2.1.1.1.1.2.21 = STRING: "CPU2 Temperature" SNMPv2-SMI::enterprises.10876.2.1.1.1.1.2.22 = STRING: "System Temperature" SNMPv2-SMI::enterprises.10876.2.1.1.1.1.2.23 = STRING: "Chassis Intrusion" SNMPv2-SMI::enterprises.10876.2.1.1.1.1.2.24 = STRING: "Power Supply Failure" SNMPv2-SMI::enterprises.10876.2.1.1.1.1.2.25 = STRING: "DIMM Temperature" SNMPv2-SMI::enterprises.10876.2.1.1.1.1.3.1 = INTEGER: 0 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.3.2 = INTEGER: 0 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.3.3 = INTEGER: 0 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.3.4 = INTEGER: 0 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.3.5 = INTEGER: 0 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.3.6 = INTEGER: 0 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.3.7 = INTEGER: 0 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.3.8 = INTEGER: 0 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.3.9 = INTEGER: 1 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.3.10 = INTEGER: 1 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.3.11 = INTEGER: 1 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.3.12 = INTEGER: 1 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.3.13 = INTEGER: 1 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.3.14 = INTEGER: 1 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.3.15 = INTEGER: 1 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.3.16 = INTEGER: 1 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.3.17 = INTEGER: 1 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.3.18 = INTEGER: 1 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.3.19 = INTEGER: 1 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.3.20 = INTEGER: 2 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.3.21 = INTEGER: 2 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.3.22 = INTEGER: 2 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.3.23 = INTEGER: 3 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.3.24 = INTEGER: 3 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.3.25 = INTEGER: 3 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.4.1 = INTEGER: 8437 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.4.2 = INTEGER: 8437 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.4.3 = INTEGER: 8437 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.4.4 = INTEGER: 8437 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.4.5 = INTEGER: 0 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.4.6 = INTEGER: 0 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.4.7 = INTEGER: 0 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.4.8 = INTEGER: 0 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.4.9 = INTEGER: 1072 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.4.10 = INTEGER: 0 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.4.11 = INTEGER: 1368 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.4.12 = INTEGER: 0 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.4.13 = INTEGER: 5120 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.4.14 = INTEGER: 5120 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.4.15 = INTEGER: 12286 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.4.16 = INTEGER: -11891 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.4.17 = INTEGER: 3264 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.4.18 = INTEGER: 3288 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.4.19 = INTEGER: 3216 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.4.20 = INTEGER: 27 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.4.21 = INTEGER: 0 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.4.22 = INTEGER: 19 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.4.23 = INTEGER: 0 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.4.24 = INTEGER: 0 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.4.25 = INTEGER: 0 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.5.9 = INTEGER: 1488 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.5.10 = INTEGER: 1488 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.5.11 = INTEGER: 1648 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.5.12 = INTEGER: 1648 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.5.13 = INTEGER: 5504 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.5.14 = INTEGER: 5504 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.5.15 = INTEGER: 13187 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.5.16 = INTEGER: -10729 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.5.17 = INTEGER: 3648 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.5.18 = INTEGER: 3648 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.5.19 = INTEGER: 3648 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.5.20 = INTEGER: 95 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.5.21 = INTEGER: 95 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.5.22 = INTEGER: 75 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.6.1 = INTEGER: 715 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.6.2 = INTEGER: 715 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.6.3 = INTEGER: 715 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.6.4 = INTEGER: 715 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.6.5 = INTEGER: 715 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.6.6 = INTEGER: 715 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.6.7 = INTEGER: 715 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.6.8 = INTEGER: 715 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.6.9 = INTEGER: 600 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.6.10 = INTEGER: 600 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.6.11 = INTEGER: 1352 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.6.12 = INTEGER: 1352 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.6.13 = INTEGER: 4512 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.6.14 = INTEGER: 4512 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.6.15 = INTEGER: 10803 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.6.16 = INTEGER: -13246 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.6.17 = INTEGER: 2952 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.6.18 = INTEGER: 2952 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.6.19 = INTEGER: 2952 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.7.1 = INTEGER: 84375 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.7.2 = INTEGER: 84375 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.7.3 = INTEGER: 84375 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.7.4 = INTEGER: 84375 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.7.5 = INTEGER: 84375 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.7.6 = INTEGER: 84375 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.7.7 = INTEGER: 84375 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.7.8 = INTEGER: 84375 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.7.9 = INTEGER: 2040 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.7.10 = INTEGER: 2040 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.7.11 = INTEGER: 2040 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.7.12 = INTEGER: 2040 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.7.13 = INTEGER: 8160 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.7.14 = INTEGER: 8160 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.7.15 = INTEGER: 13504 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.7.16 = INTEGER: 1854 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.7.17 = INTEGER: 6120 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.7.18 = INTEGER: 6120 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.7.19 = INTEGER: 6120 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.7.20 = INTEGER: 127 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.7.21 = INTEGER: 127 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.7.22 = INTEGER: 127 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.7.23 = INTEGER: 1 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.7.24 = INTEGER: 1 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.7.25 = INTEGER: 1 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.8.1 = INTEGER: 0 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.8.2 = INTEGER: 0 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.8.3 = INTEGER: 0 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.8.4 = INTEGER: 0 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.8.5 = INTEGER: 0 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.8.6 = INTEGER: 0 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.8.7 = INTEGER: 0 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.8.8 = INTEGER: 0 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.8.9 = INTEGER: 0 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.8.10 = INTEGER: 0 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.8.11 = INTEGER: 0 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.8.12 = INTEGER: 0 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.8.13 = INTEGER: 0 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.8.14 = INTEGER: 0 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.8.15 = INTEGER: 0 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.8.16 = INTEGER: -47513 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.8.17 = INTEGER: 0 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.8.18 = INTEGER: 0 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.8.19 = INTEGER: 0 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.8.20 = INTEGER: 4294967169 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.8.21 = INTEGER: 4294967169 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.8.22 = INTEGER: 4294967169 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.8.23 = INTEGER: 0 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.8.24 = INTEGER: 0 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.8.25 = INTEGER: 0 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.9.1 = INTEGER: 1 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.9.2 = INTEGER: 1 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.9.3 = INTEGER: 1 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.9.4 = INTEGER: 1 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.9.5 = INTEGER: 1 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.9.6 = INTEGER: 1 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.9.7 = INTEGER: 1 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.9.8 = INTEGER: 1 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.10.1 = INTEGER: 1 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.10.2 = INTEGER: 1 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.10.3 = INTEGER: 1 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.10.4 = INTEGER: 1 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.10.5 = INTEGER: 1 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.10.6 = INTEGER: 1 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.10.7 = INTEGER: 1 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.10.8 = INTEGER: 1 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.10.9 = INTEGER: 1 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.10.10 = INTEGER: 1 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.10.11 = INTEGER: 1 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.10.12 = INTEGER: 1 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.10.13 = INTEGER: 1 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.10.14 = INTEGER: 1 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.10.15 = INTEGER: 1 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.10.16 = INTEGER: 1 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.10.17 = INTEGER: 1 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.10.18 = INTEGER: 1 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.10.19 = INTEGER: 1 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.10.20 = INTEGER: 1 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.10.21 = INTEGER: 1 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.10.22 = INTEGER: 1 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.10.23 = INTEGER: 1 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.10.24 = INTEGER: 1 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.10.25 = INTEGER: 1
but if fails after a while with snmpbulkwalk:
[root@observium observium]# snmpbulkwalk -v2c -c 'SuperDuperPassword' box01.example.com .1.3.6.1.4.1.10876 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.2.1 = STRING: "Fan1 Fan Speed" SNMPv2-SMI::enterprises.10876.2.1.1.1.1.2.2 = STRING: "Fan2 Fan Speed" SNMPv2-SMI::enterprises.10876.2.1.1.1.1.2.3 = STRING: "Fan3 Fan Speed" SNMPv2-SMI::enterprises.10876.2.1.1.1.1.2.4 = STRING: "Fan4 Fan Speed" SNMPv2-SMI::enterprises.10876.2.1.1.1.1.2.5 = STRING: "Fan5 Fan Speed" SNMPv2-SMI::enterprises.10876.2.1.1.1.1.2.6 = STRING: "Fan6 Fan Speed" SNMPv2-SMI::enterprises.10876.2.1.1.1.1.2.7 = STRING: "Fan7 Fan Speed" SNMPv2-SMI::enterprises.10876.2.1.1.1.1.2.8 = STRING: "Fan8 Fan Speed" SNMPv2-SMI::enterprises.10876.2.1.1.1.1.2.9 = STRING: "CPU1 Vcore Voltage" SNMPv2-SMI::enterprises.10876.2.1.1.1.1.2.10 = STRING: "CPU2 Vcore Voltage" SNMPv2-SMI::enterprises.10876.2.1.1.1.1.2.11 = STRING: "CPU1 DIMM Voltage" SNMPv2-SMI::enterprises.10876.2.1.1.1.1.2.12 = STRING: "CPU2 DIMM Voltage" SNMPv2-SMI::enterprises.10876.2.1.1.1.1.2.13 = STRING: "+5V Voltage" SNMPv2-SMI::enterprises.10876.2.1.1.1.1.2.14 = STRING: "+5VSB Voltage" SNMPv2-SMI::enterprises.10876.2.1.1.1.1.2.15 = STRING: "+12V Voltage" SNMPv2-SMI::enterprises.10876.2.1.1.1.1.2.16 = STRING: "-12V Voltage" SNMPv2-SMI::enterprises.10876.2.1.1.1.1.2.17 = STRING: "+3.3V Voltage" SNMPv2-SMI::enterprises.10876.2.1.1.1.1.2.18 = STRING: "+3.3Vsb Voltage" SNMPv2-SMI::enterprises.10876.2.1.1.1.1.2.19 = STRING: "VBAT Voltage" SNMPv2-SMI::enterprises.10876.2.1.1.1.1.2.20 = STRING: "CPU1 Temperature" SNMPv2-SMI::enterprises.10876.2.1.1.1.1.2.21 = STRING: "CPU2 Temperature" SNMPv2-SMI::enterprises.10876.2.1.1.1.1.2.22 = STRING: "System Temperature" SNMPv2-SMI::enterprises.10876.2.1.1.1.1.2.23 = STRING: "Chassis Intrusion" SNMPv2-SMI::enterprises.10876.2.1.1.1.1.2.24 = STRING: "Power Supply Failure" SNMPv2-SMI::enterprises.10876.2.1.1.1.1.2.25 = STRING: "DIMM Temperature" SNMPv2-SMI::enterprises.10876.2.1.1.1.1.3.1 = INTEGER: 0 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.3.2 = INTEGER: 0 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.3.3 = INTEGER: 0 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.3.4 = INTEGER: 0 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.3.5 = INTEGER: 0 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.3.6 = INTEGER: 0 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.3.7 = INTEGER: 0 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.3.8 = INTEGER: 0 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.3.9 = INTEGER: 1 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.3.10 = INTEGER: 1 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.3.11 = INTEGER: 1 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.3.12 = INTEGER: 1 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.3.13 = INTEGER: 1 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.3.14 = INTEGER: 1 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.3.15 = INTEGER: 1 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.3.16 = INTEGER: 1 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.3.17 = INTEGER: 1 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.3.18 = INTEGER: 1 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.3.19 = INTEGER: 1 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.3.20 = INTEGER: 2 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.3.21 = INTEGER: 2 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.3.22 = INTEGER: 2 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.3.23 = INTEGER: 3 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.3.24 = INTEGER: 3 SNMPv2-SMI::enterprises.10876.2.1.1.1.1.3.25 = INTEGER: 3 Timeout: No Response from box01.example.com
Storage:
SNMP is returning storage and I'm using the linux/unix agent as well and it's echoing:
<<<df>>> /dev/md0 ext4 468688256 3227188 441653076 1% / <<<mounts>>> /dev/md0 / ext4 rw,relatime,barrier=1,data=ordered 0 0
but the graphs are not there any more. Can't find anything in the event logs either concerning storage.