Ok, I re-read full walk for your device and still not found any additional sensors with Fans and Temps (except those already discussed).
Youssef BENGELLOUN - ZAHR wrote:
Hello community,
Regarding the FAN sensors state (status / speed), JTAC confirmed MIB are missing for the newest hardware gen. They have opened a PR 1324161 to track it (see attached).
That leaves us with the rest of the missing sensors :
- Back chassis temp
- CPU temp
Mike, were you able to analyze the traces I sent you ?
Best regards.
Le 24/11/2017 09:31, « Youssef BENGELLOUN - ZAHR » ybzahr@prodware.fr a écrit :
Hello Mike, Your last email didn’t mention that, doesn’t matter. Requested outputs can be found here : https://dl.prodware.org/zljh (password : observium) Please note that for the second OID, device times out : root@prod-monit-002:/opt/observium# snmpbulkwalk -v 2c -c XYZ -On fw01-par01 .1.3.6.1.4.1.2636 > snmpbulkwalk-1361412636.txt Timeout: No Response from fw01-par01 Waiting for your feedback. Best regards. Le 24/11/2017 08:16, « observium au nom de Mike Stupalov » <observium-bounces@observium.org au nom de mike@observium.org> a écrit : Youssef BENGELLOUN - ZAHR wrote: > > Hello Mike, > > > What is your take on this ? About what? You did not send the information I wrote (please re-read my previous mail). ... Pls send me another full walk from device, I will try to find if here exist another Oids with Temp. 2 commands: snmpbulkwalk -v2c -c <community> -On <host> .1.3.6.1.2.1 snmpbulkwalk -v2c -c <community> -On <host> .1.3.6.1.4.1.2636 > > Best regards. > > > > Le 23 nov. 2017 à 10:57, Mike Stupalov <mike@observium.org > <mailto:mike@observium.org>> a écrit : > >> Wheel.. >> >> Youssef BENGELLOUN - ZAHR wrote: >>> >>> Hello Adam, >>> >>> >>> >>> It appears I got mixed up copying the wrong email output. That is what >>> happens when you do it while you are mobile and in between things. >>> My bad. >>> >>> >>> >>> So let’s take a step back here : >>> >>> >>> >>> _1/ regarding CPU temps :_ >>> >>> >>> >>> You are right about those two objects >>> (.1.3.6.1.4.1.2636.3.1.13.1.7.9.1.0.0 / >>> .1.3.6.1.4.1.2636.3.1.13.1.7.9.2.0.0), they are being queried >>> correctly and match with Chassis Temp1 - Front : >>> >>> >>> >>> https://apps.juniper.net/mib-explorer/search.jsp#object=1.3.6.1.4.1.2636.3.1.13.1.7&product=Junos%20OS&release=15.1x49-D120 >>> <https://apps.juniper.net/mib-explorer/search.jsp#object=1.3.6.1.4.1.2636.3.1.13.1.7&product=Junos%20OS&release=15.1x49-D120> >>> <https://apps.juniper.net/mib-explorer/search.jsp#object=1.3.6.1.4.1.2636.3.1.13.1.7&product=Junos%20OS&release=15.1x49-D120 >>> <https://apps.juniper.net/mib-explorer/search.jsp#object=1.3.6.1.4.1.2636.3.1.13.1.7&product=Junos%20OS&release=15.1x49-D120>> >>> >>> >>> >>> What is missing here are the following highlighted entries in Yellow : >>> >>> >>> >>> root@fw01-par01> show chassis environment >>> >>> node0: >>> >>> -------------------------------------------------------------------------- >>> >>> Class Item Status Measurement >>> >>> Power FPC 0 Power Supply 0 OK >>> >>> FPC 0 Power Supply 1 OK >>> >>> Temp System Temp1 - Front OK 30 degrees C / 86 >>> degrees F >>> >>> System Temp2 - Back OK 40 degrees C / >>> 104 degrees F >>> >>> CPU0 Temp OK 70 degrees C / >>> 158 degrees F >>> >>> CPU1 Temp OK 61 degrees C / >>> 141 degrees F >>> >>> Fans FPC 0 Fan Tray 0 OK Spinning at normal speed >>> >>> FPC 0 Fan Tray 1 OK Spinning at normal >>> speed >>> >>> FPC 0 Fan Tray 2 OK Spinning at normal >>> speed >>> >>> FPC 0 Fan Tray 3 OK Spinning at normal >>> speed >>> >>> >>> >>> I believe the rest of those entries can be found in the same MIB. If I >>> poll the whole MIB, I do get results (see attached file). Is that >>> something you can add on your end ? >>> >> >> Ok, I not see "CPUX Temp" entries inside jnxOperatingTemp Oid, here only: >> >> jnxOperatingDescr.9.1.0.0 = node0 Routing Engine >> jnxOperatingDescr.9.2.0.0 = node1 Routing Engine >> jnxOperatingTemp.9.1.0.0 = 29 >> jnxOperatingTemp.9.2.0.0 = 21 >> >> which I not sure correctly corresponded with system temp X, since here >> different values against from device CLI. >> >> Another temp sensors which I see: >> >> jnxFruName.9.1.0.0 = node0 Routing Engine >> jnxFruName.9.2.0.0 = node1 Routing Engine >> jnxFruTemp.9.1.0.0 = 30 >> jnxFruTemp.9.2.0.0 = 21 >> jnxFruType.9.1.0.0 = routingEngine >> jnxFruType.9.2.0.0 = routingEngine >> >> but this is exactly same as in jnxOperatingTemp. >> >> Pls send me another full walk from device, I will try to find if here >> exist another Oids with Temp. >> 2 commands: >> >> snmpbulkwalk -v2c -c <community> -On <host> .1.3.6.1.2.1 >> snmpbulkwalk -v2c -c <community> -On <host> .1.3.6.1.4.1.2636 >> >> >>> >>> >>> >>> >>> _2/ regarding FAN status / spinning speed :_ >>> >>> >>> >>> I was able to confirm with JTAC the correct MIB, it can be found here : >>> >>> >>> >>> https://apps.juniper.net/mib-explorer/search.jsp#object=jnxSRX4200SlotFan&product=Junos%20OS&release=15.1x49-D120 >>> <https://apps.juniper.net/mib-explorer/search.jsp#object=jnxSRX4200SlotFan&product=Junos%20OS&release=15.1x49-D120> >>> <https://apps.juniper.net/mib-explorer/search.jsp#object=jnxSRX4200SlotFan&product=Junos%20OS&release=15.1x49-D120 >>> <https://apps.juniper.net/mib-explorer/search.jsp#object=jnxSRX4200SlotFan&product=Junos%20OS&release=15.1x49-D120>> >>> >>> >>> >>> I tried with jnxSRX4200SlotFan or 1.3.6.1.4.1.2636.1.1.2.2.143.4, I >>> don’t get any answers from the device : >>> >>> >>> >>> root@prod-monit-002:~# snmpwalk -v 2c -c asp fw01-par01 >>> 1.3.6.1.4.1.2636.1.1.2.2.143.4 >>> >>> SNMPv2-SMI::enterprises.2636.1.1.2.2.143.4 = No Such Object available >>> on this agent at this OID >>> >>> >>> >>> Or >>> >>> >>> >>> root@fw01-par01> show snmp mib walk ascii jnxSRX4200SlotFan >>> >>> >>> >>> root@fw01-par01> show snmp mib walk ascii 1.3.6.1.4.1.2636.1.1.2.2.143.4 >>> >>> >>> >>> I’m having JTAC check the status of the MIB implantation. I’ll keep >>> you updated. >>> >>> >>> >>> Best regards. >>> >>> >>> >>> >>> >>> >>> >>> >>> >>> *Youssef BENGELLOUN - ZAHR* - Consultant Expert >>> Prodware France >>> T : +33 979 999 000 - F : +33 988 814 001 - ybzahr@prodware.fr >>> <mailto:ybzahr@prodware.fr> >>> <mailto:ybzahr@prodware.fr> >>> ------------------------------------------------------------------------ >>> Web : prodware.fr <http://prodware.fr> <http://www.prodware.fr> >>> <http://twitter.com/Prodware/> <http://www.facebook.com/Prodware/> >>> <https://www.linkedin.com/company/prodwarefrance> >>> <https://www.youtube.com/c/ProdwareFrance> >>> <http://www.viadeo.com/fr/company/prodware> >>> <http://www.prodware.fr/social-network/> >>> >>> >>> >>> *De : *observium <observium-bounces@observium.org >>> <mailto:observium-bounces@observium.org>> au nom de Adam >>> Armstrong <adama@observium.org <mailto:adama@observium.org>> >>> *Répondre à : *Observium <observium@observium.org >>> <mailto:observium@observium.org>> >>> *Date : *mercredi 22 novembre 2017 à 22:47 >>> *À : *"observium@observium.org <mailto:observium@observium.org>" >>> <observium@observium.org <mailto:observium@observium.org>> >>> *Objet : *Re: [Observium] SRX4200 FAN status missing >>> >>> >>> >>> Both of those sensors are polled: >>> >>> >>> >>> CMD[/usr/bin/snmpget -v2c -c *** -Pu -OQUsn -M /opt/observium/mibs >>> 'udp':'fw01-par01':'161' .1.3.6.1.4.1.2636.3.1.13.1.7.9.1.0.0 >>> .1.3.6.1.4.1.2636.3.1.13.1.7.9.2.0.0] >>> >>> >>> >>> CMD EXITCODE[0] >>> >>> CMD RUNTIME[0.0178s] >>> >>> STDOUT[ >>> >>> .1.3.6.1.4.1.2636.3.1.13.1.7.9.1.0.0 = 29 >>> >>> .1.3.6.1.4.1.2636.3.1.13.1.7.9.2.0.0 = 21 >>> >>> ] >>> >>> SNMP STATUS[TRUE] >>> >>> >>> >>> DescrClass >>> >>> TypeOrigin >>> >>> ValueEvent >>> >>> Last Changed >>> >>> node0 Routing Engine temperaturejunos >>> >>> snmp29C >>> >>> ok2017-02-02 11:40:44 >>> >>> node1 Routing Engine temperaturejunos >>> >>> snmp21C >>> >>> ok2017-10-01 07:00:02 >>> >>> >>> >>> adam. >>> >>> >>> >>> Adam Armstrong >>> >>> Managing Director & Lead Architect >>> >>> Observium Limited >>> >>> http://www.observium.org >>> >>> http://docs.observium.org >>> >>> http://jira.observium.org >>> >>> On 2017-11-22 21:43:53, Youssef BENGELLOUN - ZAHR >>> <ybzahr@prodware.fr <mailto:ybzahr@prodware.fr>> wrote: >>> >>> I’m not seeing them in the device page. >>> >>> >>> >>> Moreover, no mention at all in the poller output in debug output I >>> provided with my initial email. >>> >>> >>> >>> What kind of trace do you want me to run ? >>> >>> >>> >>> Best regards. >>> >>> >>> >>> >>> Le 22 nov. 2017 à 22:22, Adam Armstrong <adama@observium.org >>> <mailto:adama@observium.org> >>> <mailto:adama@observium.org>> a écrit : >>> >>> The process of collecting temperature sensors from this table >>> certainly works for me. >>> >>> >>> >>> The only requirement in the code seems to be that the value >>> returned isn't zero. >>> >>> >>> >>> Are you /sure/ these sensors aren't being discovered? >>> >>> >>> >>> adam. >>> >>> >>> >>> Adam Armstrong >>> >>> CEO & Lead Architect >>> >>> Observium Limited >>> >>> On 2017-11-22 21:14:23, Youssef BENGELLOUN - ZAHR >>> <ybzahr@prodware.fr <mailto:ybzahr@prodware.fr> >>> <mailto:ybzahr@prodware.fr>> wrote: >>> >>> CPUs temps (2x units) from race node : >>> >>> >>> >>> root@fw01-par01> show chassis environment >>> >>> node0: >>> >>> -------------------------------------------------------------------------- >>> >>> Class Item Status Measurement >>> >>> Power FPC 0 Power Supply 0 OK >>> >>> FPC 0 Power Supply 1 OK >>> >>> Temp System Temp1 - Front OK 29 degrees >>> C / 84 degrees F >>> >>> System Temp2 - Back OK 39 degrees >>> C / 102 degrees F >>> >>> CPU0 Temp OK 70 degrees >>> C / 158 degrees F >>> >>> CPU1 Temp OK 61 degrees >>> C / 141 degrees F >>> >>> >>> >>> >>> >>> Best regards. >>> >>> >>> >>> >>> >>> >>> Le 22 nov. 2017 à 21:53, Adam Armstrong >>> <adama@observium.org <mailto:adama@observium.org> >>> <mailto:adama@observium.org>> a écrit : >>> >>> What is the inventory entry referred to by the >>> indexes 9.1.0.0 and 9.2.0.0? >>> >>> >>> >>> We should definitely already see temperatures from here. >>> >>> >>> >>> BTW, i honestly tend to ignore walks without MIBs >>> loaded. I can easily work out what a numerical OID is >>> from the text, but it's not so useful the other way. >>> >>> >>> >>> adam. >>> >>> >>> >>> Adam Armstrong >>> >>> CEO & Lead Architect >>> >>> Observium Limited >>> >>> On 2017-11-22 19:29:22, Youssef BENGELLOUN - ZAHR >>> <ybzahr@prodware.fr <mailto:ybzahr@prodware.fr> >>> <mailto:ybzahr@prodware.fr>> >>> wrote: >>> >>> Hi, >>> >>> From Observium box, there you go : >>> >>> root@prod-monit-002:~# snmpwalk -v 2c -c asp >>> fw01-par01 1.3.6.1.4.1.2636.4.1.2 >>> SNMPv2-SMI::enterprises.2636.4.1.2 = No Such >>> Object available on this agent at this OID >>> >>> ⇒No answer regarding FANs. >>> >>> >>> root@prod-monit-002:~# snmpwalk -v 2c -c asp >>> fw01-par01 1.3.6.1.4.1.2636.3.1.13.1.7 >>> SNMPv2-SMI::enterprises.2636.3.1.13.1.7.1.1.0.0 = >>> Gauge32: 0 >>> SNMPv2-SMI::enterprises.2636.3.1.13.1.7.1.2.0.0 = >>> Gauge32: 0 >>> SNMPv2-SMI::enterprises.2636.3.1.13.1.7.2.1.1.0 = >>> Gauge32: 0 >>> SNMPv2-SMI::enterprises.2636.3.1.13.1.7.2.1.2.0 = >>> Gauge32: 0 >>> SNMPv2-SMI::enterprises.2636.3.1.13.1.7.2.2.1.0 = >>> Gauge32: 0 >>> SNMPv2-SMI::enterprises.2636.3.1.13.1.7.2.2.2.0 = >>> Gauge32: 0 >>> SNMPv2-SMI::enterprises.2636.3.1.13.1.7.7.1.0.0 = >>> Gauge32: 0 >>> SNMPv2-SMI::enterprises.2636.3.1.13.1.7.7.2.0.0 = >>> Gauge32: 0 >>> SNMPv2-SMI::enterprises.2636.3.1.13.1.7.8.1.1.0 = >>> Gauge32: 0 >>> SNMPv2-SMI::enterprises.2636.3.1.13.1.7.8.2.1.0 = >>> Gauge32: 0 >>> SNMPv2-SMI::enterprises.2636.3.1.13.1.7.9.1.0.0 = >>> Gauge32: 29 >>> SNMPv2-SMI::enterprises.2636.3.1.13.1.7.9.1.1.0 = >>> Gauge32: 0 >>> SNMPv2-SMI::enterprises.2636.3.1.13.1.7.9.2.0.0 = >>> Gauge32: 23 >>> SNMPv2-SMI::enterprises.2636.3.1.13.1.7.9.2.1.0 = >>> Gauge32: 0 >>> >>> ⇒Answers are returned regarding CPU temps. >>> >>> >>> Best regards. >>> >>> >>> >>> Le 22/11/2017 20:23, « observium au nom de Michael >>> » a écrit : >>> >>> Youseff, >>> >>> By now you should know that there can be a world >>> of difference between what the cli of a device can >>> tell you and what it actually presents out the >>> snmp stack. >>> >>> Try running the queries to the oids from a remote >>> host (such as from your observium box). >>> >>> If it doesn't respond to the queries, there's not >>> much that can be done. >>> >>> Michael >>> >>> >>> >>> On 23 November 2017 6:02:39 AM AEDT, Youssef >>> BENGELLOUN - ZAHR wrote: >>>> >>> >>> BENGELLOUN - ZAHR Youssef - Consultant Expert >>> Prodware France >>> T : +33 979 999 000 F : +33 988 814 001 - >>> ybzahr@prodware.fr <mailto:ybzahr@prodware.fr> >>> <mailto:ybzahr@prodware.fr> >>> Web : prodware.fr <http://prodware.fr> >>> <http://prodware.fr> >>> >>> >>> >>> >>> *Youssef BENGELLOUN - ZAHR* - Consultant Expert >>> Prodware France >>> T : +33 979 999 000 - F : +33 988 814 001 - >>> ybzahr@prodware.fr <mailto:ybzahr@prodware.fr> >>> <mailto:ybzahr@prodware.fr> >>> >>> ------------------------------------------------------------------------ >>> >>> >>> >>> Web : prodware.fr <http://prodware.fr> >>> <http://www.prodware.fr> >>> >>> <http://twitter.com/Prodware/> >>> <http://www.facebook.com/Prodware/> >>> <https://www.linkedin.com/company/prodwarefrance> >>> <https://www.youtube.com/c/ProdwareFrance> >>> <http://www.viadeo.com/fr/company/prodware> >>> <http://www.prodware.fr/social-network/> >>> >>> >>> >>> >>> >>> *Youssef BENGELLOUN - ZAHR* - Consultant Expert >>> Prodware France >>> T : +33 979 999 000 - F : +33 988 814 001 - ybzahr@prodware.fr >>> <mailto:ybzahr@prodware.fr> >>> <mailto:ybzahr@prodware.fr> >>> >>> ------------------------------------------------------------------------ >>> >>> >>> >>> Web : prodware.fr <http://prodware.fr> <http://www.prodware.fr> >>> >>> <http://twitter.com/Prodware/> >>> <http://www.facebook.com/Prodware/> >>> <https://www.linkedin.com/company/prodwarefrance> >>> <https://www.youtube.com/c/ProdwareFrance> >>> <http://www.viadeo.com/fr/company/prodware> >>> <http://www.prodware.fr/social-network/> >>> >>> >>> >>> > > > > *Youssef BENGELLOUN - ZAHR* - Consultant Expert > Prodware France > T : +33 979 999 000 - F : +33 988 814 001 - ybzahr@prodware.fr > <mailto:ybzahr@prodware.fr> > ------------------------------------------------------------------------ > Web : prodware.fr <http://www.prodware.fr> > <http://twitter.com/Prodware/> <http://www.facebook.com/Prodware/> > <https://www.linkedin.com/company/prodwarefrance> > <https://www.youtube.com/c/ProdwareFrance> > <http://www.viadeo.com/fr/company/prodware> > <http://www.prodware.fr/social-network/> > > > >>>BENGELLOUN - ZAHR Youssef - Consultant Expert Prodware France T : +33 979 999 000 F : +33 988 814 001 - ybzahr@prodware.fr Web : prodware.fr
>>>> observium mailing list >>>> observium@observium.org <mailto:observium@observium.org> >>> <mailto:observium@observium.org> >>>> http://postman.memetic.org/cgi-bin/mailman/listinfo/observium >>> >>> _______________________________________________ >>> observium mailing list >>> observium@observium.org >>> <mailto:observium@observium.org> >>> <mailto:observium@observium.org> >>> http://postman.memetic.org/cgi-bin/mailman/listinfo/observium >>> >>> >>> >>> _______________________________________________ >>> observium mailing list >>> observium@observium.org >>> <mailto:observium@observium.org> >>> <mailto:observium@observium.org> >>> http://postman.memetic.org/cgi-bin/mailman/listinfo/observium >>> >>> _______________________________________________ >>> observium mailing list >>> observium@observium.org >>> <mailto:observium@observium.org> <mailto:observium@observium.org> >>> http://postman.memetic.org/cgi-bin/mailman/listinfo/observium >>> >>> _______________________________________________ >>> observium mailing list >>> observium@observium.org <mailto:observium@observium.org> >>> <mailto:observium@observium.org> >>> http://postman.memetic.org/cgi-bin/mailman/listinfo/observium >>> >>> _______________________________________________ >>> observium mailing list >>> observium@observium.org <mailto:observium@observium.org> >>> http://postman.memetic.org/cgi-bin/mailman/listinfo/observium >> >> -- >> Mike Stupalov >> Observium Limited, http://observium.org >> _______________________________________________ >> observium mailing list >> observium@observium.org <mailto:observium@observium.org> >> http://postman.memetic.org/cgi-bin/mailman/listinfo/observium > _______________________________________________ > observium mailing list > observium@observium.org > http://postman.memetic.org/cgi-bin/mailman/listinfo/observium -- Mike Stupalov Observium Limited, http://observium.org _______________________________________________ observium mailing list observium@observium.org http://postman.memetic.org/cgi-bin/mailman/listinfo/observium
observium mailing list observium@observium.org http://postman.memetic.org/cgi-bin/mailman/listinfo/observium