Thanks for the response. I hear what you are saying about date compares, but it seems like Observium is already manipulating the response. I say this because the string in the UI, it says:

 

Diagnostics Results (last 2022-10-10)                        ok

 

But the actual returned string from the device via SNMP:

 

# snmpget -v2c -c [redacted community] [redacted host name]  .1.3.6.1.4.1.318.1.1.1.7.2.4.0

iso.3.6.1.4.1.318.1.1.1.7.2.4.0 = STRING: "10/10/2022"

 

I think what I am saying is, observium doesn’t seem to be handling it as an arbitrary value.

 

 

 

 

 

 

 

From: Adam Armstrong via observium <observium@lists.observium.org>
Sent: Monday, October 10, 2022 11:03 AM
To: Alex Rubenstein via observium <observium@lists.observium.org>
Cc: Adam Armstrong <adama@observium.org>
Subject: [Observium] Re: APC UPS Monitoring

 

The only way to do this would be to create a probe that fetches the value and does the calculations on it. You could likely do this in PHP or python or whatever.

You could also create a custom status indicator that extracts this in PHP, but the probe might be easier.

Imagine trying to write a UI to extract an arbitrary value from a text string and then do date matching on it!

adam.

Alex Rubenstein via observium wrote on 2022-10-10 15:59:

One of the status indicators on APC UPS’s is “Diagnostic Results.” It is shown as:

 

Diagnostics Results (last 2022-10-10)                        ok

 

I am looking to set up an alert where if the last diag date is more than N days ago, alert me. But since the date is somehow wrapped into the status name, rather than the status result, I am not sure how to do this.

 

Any pointers?

 

 




_______________________________________________
observium mailing list -- observium@lists.observium.org
To unsubscribe send an email to observium-leave@lists.observium.org

 

--

Sent from Postbox