I would like to graph the air temp and air flow in these in row cooling units. I see some APC ups support but not these units. Any pointers on how I would go about it? I am willing to do the leg work. I just don't know how to start. Here is the info on the unit. http://www.apc.com/resource/include/techspec_index.cfm?base_sku=ACRC500&...
Bruce
I would recommend seeing if you can find a MIB definition/file for this unit.
Thanks, Scott Brawner Description: cid:image002.jpg@01CBD278.0CADB410
From: observium [mailto:observium-bounces@observium.org] On Behalf Of Bruce Winters Sent: Saturday, February 15, 2014 10:48 PM To: Observium Network Observation System Subject: [Observium] APC InRow Cooling support
I would like to graph the air temp and air flow in these in row cooling units. I see some APC ups support but not these units. Any pointers on how I would go about it? I am willing to do the leg work. I just don't know how to start. Here is the info on the unit. http://www.apc.com/resource/include/techspec_index.cfm?base_sku=ACRC500 http://www.apc.com/resource/include/techspec_index.cfm?base_sku=ACRC500&tab =software &tab=software
Bruce
It's probably just PowerNet-MIB. We already do a little of the in-row chiller stuff, I also have half a rewrite pending when I find some time to finish it, that may already solve the problem.. or maybe not, if it's in yet another part of the MIB tree :-)
Tom
On 02/17/2014 02:11 PM, Scott Brawner wrote:
I would recommend seeing if you can find a MIB definition/file for this unit...
Thanks, Scott Brawner Description: cid:image002.jpg@01CBD278.0CADB410
*From:*observium [mailto:observium-bounces@observium.org] *On Behalf Of *Bruce Winters *Sent:* Saturday, February 15, 2014 10:48 PM *To:* Observium Network Observation System *Subject:* [Observium] APC InRow Cooling support
I would like to graph the air temp and air flow in these in row cooling units. I see some APC ups support but not these units. Any pointers on how I would go about it? I am willing to do the leg work. I just don't know how to start. Here is the info on the unit. http://www.apc.com/resource/include/techspec_index.cfm?base_sku=ACRC500&...
Bruce
observium mailing list observium@observium.org http://postman.memetic.org/cgi-bin/mailman/listinfo/observium
It uses the APC PowerNet MIB. I was able to add one of the units but it shows up as a generic device. It is graphing the ethernet interface. Any advice as to what to do next? On Feb 17, 2014 8:20 AM, "Scott Brawner" Scott.Brawner@kratosdefense.com wrote:
I would recommend seeing if you can find a MIB definition/file for this unit...
Thanks, Scott Brawner [image: Description: cid:image002.jpg@01CBD278.0CADB410]
*From:* observium [mailto:observium-bounces@observium.org] *On Behalf Of *Bruce Winters *Sent:* Saturday, February 15, 2014 10:48 PM *To:* Observium Network Observation System *Subject:* [Observium] APC InRow Cooling support
I would like to graph the air temp and air flow in these in row cooling units. I see some APC ups support but not these units. Any pointers on how I would go about it? I am willing to do the leg work. I just don't know how to start. Here is the info on the unit. http://www.apc.com/resource/include/techspec_index.cfm?base_sku=ACRC500&...
Bruce
observium mailing list observium@observium.org http://postman.memetic.org/cgi-bin/mailman/listinfo/observium
Is there something I can do to help you? I would like to get involved in the Observium project. On Feb 17, 2014 8:39 AM, "Bruce Winters" bruce.winters@gmail.com wrote:
It uses the APC PowerNet MIB. I was able to add one of the units but it shows up as a generic device. It is graphing the ethernet interface. Any advice as to what to do next? On Feb 17, 2014 8:20 AM, "Scott Brawner" Scott.Brawner@kratosdefense.com wrote:
I would recommend seeing if you can find a MIB definition/file for this unit...
Thanks, Scott Brawner [image: Description: cid:image002.jpg@01CBD278.0CADB410]
*From:* observium [mailto:observium-bounces@observium.org] *On Behalf Of *Bruce Winters *Sent:* Saturday, February 15, 2014 10:48 PM *To:* Observium Network Observation System *Subject:* [Observium] APC InRow Cooling support
I would like to graph the air temp and air flow in these in row cooling units. I see some APC ups support but not these units. Any pointers on how I would go about it? I am willing to do the leg work. I just don't know how to start. Here is the info on the unit. http://www.apc.com/resource/include/techspec_index.cfm?base_sku=ACRC500&...
Bruce
observium mailing list observium@observium.org http://postman.memetic.org/cgi-bin/mailman/listinfo/observium
Bruce,
If it shows up as a generic device, it won't poll PowerNet-MIB. Needs to be recognized as APC.
We currently recognize APC by (includes/definitions/os.inc.php): $config['os'][$os]['sysObjectID'][] = ".1.3.6.1.4.1.318.1";
What's your device's sysObjectID?
Tom
On 02/17/2014 02:51 PM, Bruce Winters wrote:
Is there something I can do to help you? I would like to get involved in the Observium project.
On Feb 17, 2014 8:39 AM, "Bruce Winters" <bruce.winters@gmail.com mailto:bruce.winters@gmail.com> wrote:
It uses the APC PowerNet MIB. I was able to add one of the units but it shows up as a generic device. It is graphing the ethernet interface. Any advice as to what to do next? On Feb 17, 2014 8:20 AM, "Scott Brawner" <Scott.Brawner@kratosdefense.com <mailto:Scott.Brawner@kratosdefense.com>> wrote: I would recommend seeing if you can find a MIB definition/file for this unit... Thanks, Scott Brawner Description: cid:image002.jpg@01CBD278.0CADB410 *From:*observium [mailto:observium-bounces@observium.org <mailto:observium-bounces@observium.org>] *On Behalf Of *Bruce Winters *Sent:* Saturday, February 15, 2014 10:48 PM *To:* Observium Network Observation System *Subject:* [Observium] APC InRow Cooling support I would like to graph the air temp and air flow in these in row cooling units. I see some APC ups support but not these units. Any pointers on how I would go about it? I am willing to do the leg work. I just don't know how to start. Here is the info on the unit. http://www.apc.com/resource/include/techspec_index.cfm?base_sku=ACRC500&tab=software Bruce _______________________________________________ observium mailing list observium@observium.org <mailto:observium@observium.org> http://postman.memetic.org/cgi-bin/mailman/listinfo/observium
observium mailing list observium@observium.org http://postman.memetic.org/cgi-bin/mailman/listinfo/observium
Tom,
System sysObjectID -> .1.3.6.1.4.1.318.7.1.3.14
Bruce On Feb 17, 2014 9:50 AM, "Tom Laermans" tom.laermans@powersource.cx wrote:
Bruce,
If it shows up as a generic device, it won't poll PowerNet-MIB. Needs to be recognized as APC.
We currently recognize APC by (includes/definitions/os.inc.php): $config['os'][$os]['sysObjectID'][] = ".1.3.6.1.4.1.318.1";
What's your device's sysObjectID?
Tom
On 02/17/2014 02:51 PM, Bruce Winters wrote:
Is there something I can do to help you? I would like to get involved in the Observium project. On Feb 17, 2014 8:39 AM, "Bruce Winters" bruce.winters@gmail.com wrote:
It uses the APC PowerNet MIB. I was able to add one of the units but it shows up as a generic device. It is graphing the ethernet interface. Any advice as to what to do next? On Feb 17, 2014 8:20 AM, "Scott Brawner" Scott.Brawner@kratosdefense.com wrote:
I would recommend seeing if you can find a MIB definition/file for this unit...
Thanks, Scott Brawner [image: Description: cid:image002.jpg@01CBD278.0CADB410]
*From:* observium [mailto:observium-bounces@observium.org] *On Behalf Of *Bruce Winters *Sent:* Saturday, February 15, 2014 10:48 PM *To:* Observium Network Observation System *Subject:* [Observium] APC InRow Cooling support
I would like to graph the air temp and air flow in these in row cooling units. I see some APC ups support but not these units. Any pointers on how I would go about it? I am willing to do the leg work. I just don't know how to start. Here is the info on the unit. http://www.apc.com/resource/include/techspec_index.cfm?base_sku=ACRC500&...
Bruce
observium mailing list observium@observium.org http://postman.memetic.org/cgi-bin/mailman/listinfo/observium
observium mailing listobservium@observium.orghttp://postman.memetic.org/cgi-bin/mailman/listinfo/observium
observium mailing list observium@observium.org http://postman.memetic.org/cgi-bin/mailman/listinfo/observium
Here is the sysid and some other info.
6d 16h 12m System sysDescr -> APC Web/SNMP Management Card (MB:v3.9.2 PF:v3.7.3 PN:apc_hw03_aos_373.bin AF1:v3.7.1 AN1:apc_hw03_acrp_371.bin MN:ACRC500 HR:04 SN: JK1337Xxxxx MD:09/14/2013) 6d 16h 12m System sysName -> unknown 6d 16h 12m System sysObjectID -> .1.3.6.1.4.1.318.7.1.3.14 On Feb 17, 2014 8:51 AM, "Bruce Winters" bruce.winters@gmail.com wrote:
Is there something I can do to help you? I would like to get involved in the Observium project. On Feb 17, 2014 8:39 AM, "Bruce Winters" bruce.winters@gmail.com wrote:
It uses the APC PowerNet MIB. I was able to add one of the units but it shows up as a generic device. It is graphing the ethernet interface. Any advice as to what to do next? On Feb 17, 2014 8:20 AM, "Scott Brawner" Scott.Brawner@kratosdefense.com wrote:
I would recommend seeing if you can find a MIB definition/file for this unit...
Thanks, Scott Brawner [image: Description: cid:image002.jpg@01CBD278.0CADB410]
*From:* observium [mailto:observium-bounces@observium.org] *On Behalf Of *Bruce Winters *Sent:* Saturday, February 15, 2014 10:48 PM *To:* Observium Network Observation System *Subject:* [Observium] APC InRow Cooling support
I would like to graph the air temp and air flow in these in row cooling units. I see some APC ups support but not these units. Any pointers on how I would go about it? I am willing to do the leg work. I just don't know how to start. Here is the info on the unit. http://www.apc.com/resource/include/techspec_index.cfm?base_sku=ACRC500&...
Bruce
observium mailing list observium@observium.org http://postman.memetic.org/cgi-bin/mailman/listinfo/observium
Bruce,
Weird sysObjectID. :-) Try an update to 5001!
Tom
On 02/17/2014 03:46 PM, Bruce Winters wrote:
Here is the sysid and some other info.
6d 16h 12m System sysDescr -> APC Web/SNMP Management Card (MB:v3.9.2 PF:v3.7.3 PN:apc_hw03_aos_373.bin AF1:v3.7.1 AN1:apc_hw03_acrp_371.bin MN:ACRC500 HR:04 SN: JK1337Xxxxx MD:09/14/2013) 6d 16h 12m System sysName -> unknown 6d 16h 12m System sysObjectID -> .1.3.6.1.4.1.318.7.1.3.14
On Feb 17, 2014 8:51 AM, "Bruce Winters" <bruce.winters@gmail.com mailto:bruce.winters@gmail.com> wrote:
Is there something I can do to help you? I would like to get involved in the Observium project. On Feb 17, 2014 8:39 AM, "Bruce Winters" <bruce.winters@gmail.com <mailto:bruce.winters@gmail.com>> wrote: It uses the APC PowerNet MIB. I was able to add one of the units but it shows up as a generic device. It is graphing the ethernet interface. Any advice as to what to do next? On Feb 17, 2014 8:20 AM, "Scott Brawner" <Scott.Brawner@kratosdefense.com <mailto:Scott.Brawner@kratosdefense.com>> wrote: I would recommend seeing if you can find a MIB definition/file for this unit... Thanks, Scott Brawner Description: cid:image002.jpg@01CBD278.0CADB410 *From:*observium [mailto:observium-bounces@observium.org <mailto:observium-bounces@observium.org>] *On Behalf Of *Bruce Winters *Sent:* Saturday, February 15, 2014 10:48 PM *To:* Observium Network Observation System *Subject:* [Observium] APC InRow Cooling support I would like to graph the air temp and air flow in these in row cooling units. I see some APC ups support but not these units. Any pointers on how I would go about it? I am willing to do the leg work. I just don't know how to start. Here is the info on the unit. http://www.apc.com/resource/include/techspec_index.cfm?base_sku=ACRC500&tab=software Bruce _______________________________________________ observium mailing list observium@observium.org <mailto:observium@observium.org> http://postman.memetic.org/cgi-bin/mailman/listinfo/observium
observium mailing list observium@observium.org http://postman.memetic.org/cgi-bin/mailman/listinfo/observium
participants (3)
-
Bruce Winters
-
Scott Brawner
-
Tom Laermans