Alert check config for a UPS "Status" entry
![](https://secure.gravatar.com/avatar/eece35488ccb927fb242176d3a8622f0.jpg?s=120&d=mm&r=g)
We'd like to alert when any of our APC UPS'es output status is not "online"
I see an alert check type is "status" but I'm not sure what to use for the other settings.
Right now we have a UPS in hardware bypass due to a bad inverter (ugh) and the status entry says "event alert, status hardwareFailureBypass".
Any tips?
*Spencer Ryan* | Senior Systems Administrator | sryan@arbor.net *Arbor Networks* +1.734.794.5033 (d) | +1.734.846.2053 (m) www.arbornetworks.com
![](https://secure.gravatar.com/avatar/defdef53b588cb6b5f6b09e33764723a.jpg?s=120&d=mm&r=g)
You can alert when the value does not equal 2 (from the looks of it)
Maarten -- Maarten Moerman | Mgr, Network Engineering | eBay Classifieds | +31-655122247 | mmoerman@ebay.com
From: observium on behalf of Spencer Ryan Reply-To: Observium Network Observation System Date: Monday, February 8, 2016 at 3:03 PM To: Observium Network Observation System Subject: [Observium] Alert check config for a UPS "Status" entry
We'd like to alert when any of our APC UPS'es output status is not "online"
I see an alert check type is "status" but I'm not sure what to use for the other settings.
Right now we have a UPS in hardware bypass due to a bad inverter (ugh) and the status entry says "event alert, status hardwareFailureBypass".
Any tips?
Spencer Ryan | Senior Systems Administrator | sryan@arbor.netmailto:sryan@arbor.net Arbor Networks +1.734.794.5033 (d) | +1.734.846.2053 (m) www.arbornetworks.comhttp://www.arbornetworks.com/
![](https://secure.gravatar.com/avatar/eece35488ccb927fb242176d3a8622f0.jpg?s=120&d=mm&r=g)
Looks like I could, although rather than guessing random numbers it would be nice if I could reference the statues such as "*hardwareFailureBypass"*
*Spencer Ryan* | Senior Systems Administrator | sryan@arbor.net *Arbor Networks* +1.734.794.5033 (d) | +1.734.846.2053 (m) www.arbornetworks.com
On Mon, Feb 8, 2016 at 9:05 AM, Moerman, Maarten mmoerman@ebay.com wrote:
You can alert when the value does not equal 2 (from the looks of it)
Maarten
Maarten Moerman | Mgr, Network Engineering | eBay Classifieds | +31-655122247 | mmoerman@ebay.com
From: observium on behalf of Spencer Ryan Reply-To: Observium Network Observation System Date: Monday, February 8, 2016 at 3:03 PM To: Observium Network Observation System Subject: [Observium] Alert check config for a UPS "Status" entry
We'd like to alert when any of our APC UPS'es output status is not "online"
I see an alert check type is "status" but I'm not sure what to use for the other settings.
Right now we have a UPS in hardware bypass due to a bad inverter (ugh) and the status entry says "event alert, status hardwareFailureBypass".
Any tips?
- Spencer Ryan* | Senior Systems Administrator | sryan@arbor.net
*Arbor Networks* +1.734.794.5033 (d) | +1.734.846.2053 (m) www.arbornetworks.com
observium mailing list observium@observium.org http://postman.memetic.org/cgi-bin/mailman/listinfo/observium
![](https://secure.gravatar.com/avatar/defdef53b588cb6b5f6b09e33764723a.jpg?s=120&d=mm&r=g)
I guess your MIB file can tell you.
Maarten -- Maarten Moerman | Mgr, Network Engineering | eBay Classifieds | +31-655122247 | mmoerman@ebay.com
From: observium on behalf of Spencer Ryan Reply-To: Observium Network Observation System Date: Monday, February 8, 2016 at 3:08 PM To: Observium Network Observation System Subject: Re: [Observium] Alert check config for a UPS "Status" entry
Looks like I could, although rather than guessing random numbers it would be nice if I could reference the statues such as "hardwareFailureBypass"
Spencer Ryan | Senior Systems Administrator | sryan@arbor.netmailto:sryan@arbor.net Arbor Networks +1.734.794.5033 (d) | +1.734.846.2053 (m) www.arbornetworks.comhttp://www.arbornetworks.com/
On Mon, Feb 8, 2016 at 9:05 AM, Moerman, Maarten <mmoerman@ebay.commailto:mmoerman@ebay.com> wrote: You can alert when the value does not equal 2 (from the looks of it)
Maarten -- Maarten Moerman | Mgr, Network Engineering | eBay Classifieds | +31-655122247tel:%2B31-655122247 | mmoerman@ebay.commailto:mmoerman@ebay.com
From: observium on behalf of Spencer Ryan Reply-To: Observium Network Observation System Date: Monday, February 8, 2016 at 3:03 PM To: Observium Network Observation System Subject: [Observium] Alert check config for a UPS "Status" entry
We'd like to alert when any of our APC UPS'es output status is not "online"
I see an alert check type is "status" but I'm not sure what to use for the other settings.
Right now we have a UPS in hardware bypass due to a bad inverter (ugh) and the status entry says "event alert, status hardwareFailureBypass".
Any tips?
Spencer Ryan | Senior Systems Administrator | sryan@arbor.netmailto:sryan@arbor.net Arbor Networks +1.734.794.5033tel:%2B1.734.794.5033 (d) | +1.734.846.2053tel:%2B1.734.846.2053 (m) www.arbornetworks.comhttp://www.arbornetworks.com/
_______________________________________________ observium mailing list observium@observium.orgmailto:observium@observium.org http://postman.memetic.org/cgi-bin/mailman/listinfo/observium
![](https://secure.gravatar.com/avatar/21caf0a08d095be7196a1648d20942be.jpg?s=120&d=mm&r=g)
I'd just alert on "status_event notequals up" to catch all fail states, unless you really want separate checkers/contacts depending on what's wrong with the thing :)
On 2016-02-08 15:05, Moerman, Maarten wrote:
You can alert when the value does not equal 2 (from the looks of it)
Maarten
Maarten Moerman | Mgr, Network Engineering | eBay Classifieds | +31-655122247 | mmoerman@ebay.com
From: observium on behalf of Spencer Ryan Reply-To: Observium Network Observation System Date: Monday, February 8, 2016 at 3:03 PM To: Observium Network Observation System Subject: [Observium] Alert check config for a UPS "Status" entry
We'd like to alert when any of our APC UPS'es output status is not "online"
I see an alert check type is "status" but I'm not sure what to use for the other settings.
Right now we have a UPS in hardware bypass due to a bad inverter (ugh) and the status entry says "event alert, status hardwareFailureBypass".
Any tips?
Spencer Ryan* | Senior Systems Administrator | sryan@arbor.net mailto:sryan@arbor.net *Arbor Networks* +1.734.794.5033 (d) | +1.734.846.2053 (m) www.arbornetworks.com http://www.arbornetworks.com/
observium mailing list observium@observium.org http://postman.memetic.org/cgi-bin/mailman/listinfo/observium
![](https://secure.gravatar.com/avatar/eece35488ccb927fb242176d3a8622f0.jpg?s=120&d=mm&r=g)
Thanks Tom, that might be the smartest idea.
*Spencer Ryan* | Senior Systems Administrator | sryan@arbor.net *Arbor Networks* +1.734.794.5033 (d) | +1.734.846.2053 (m) www.arbornetworks.com
On Mon, Feb 8, 2016 at 9:10 AM, Tom Laermans tom.laermans@powersource.cx wrote:
I'd just alert on "status_event notequals up" to catch all fail states, unless you really want separate checkers/contacts depending on what's wrong with the thing :)
On 2016-02-08 15:05, Moerman, Maarten wrote:
You can alert when the value does not equal 2 (from the looks of it)
Maarten
Maarten Moerman | Mgr, Network Engineering | eBay Classifieds | +31-655122247 | mmoerman@ebay.com
From: observium on behalf of Spencer Ryan Reply-To: Observium Network Observation System Date: Monday, February 8, 2016 at 3:03 PM To: Observium Network Observation System Subject: [Observium] Alert check config for a UPS "Status" entry
We'd like to alert when any of our APC UPS'es output status is not "online"
I see an alert check type is "status" but I'm not sure what to use for the other settings.
Right now we have a UPS in hardware bypass due to a bad inverter (ugh) and the status entry says "event alert, status hardwareFailureBypass".
Any tips?
- Spencer Ryan* | Senior Systems Administrator | sryan@arbor.net
sryan@arbor.net *Arbor Networks* +1.734.794.5033 (d) | +1.734.846.2053 (m) http://www.arbornetworks.com/www.arbornetworks.com
observium mailing listobservium@observium.orghttp://postman.memetic.org/cgi-bin/mailman/listinfo/observium
observium mailing list observium@observium.org http://postman.memetic.org/cgi-bin/mailman/listinfo/observium
![](https://secure.gravatar.com/avatar/eece35488ccb927fb242176d3a8622f0.jpg?s=120&d=mm&r=g)
It may also be interesting to set an alert to trigger after some long amount of time (12 hours?) of the battery capacity being < 95% (or something reasonable).
It looks like this UPS charged the battery about 50% after a multi hour power failure and then the charger/inverter went into some internal fault and the unit switched to bypass.
*Spencer Ryan* | Senior Systems Administrator | sryan@arbor.net *Arbor Networks* +1.734.794.5033 (d) | +1.734.846.2053 (m) www.arbornetworks.com
On Mon, Feb 8, 2016 at 9:14 AM, Spencer Ryan sryan@arbor.net wrote:
Thanks Tom, that might be the smartest idea.
*Spencer Ryan* | Senior Systems Administrator | sryan@arbor.net *Arbor Networks* +1.734.794.5033 (d) | +1.734.846.2053 (m) www.arbornetworks.com
On Mon, Feb 8, 2016 at 9:10 AM, Tom Laermans tom.laermans@powersource.cx wrote:
I'd just alert on "status_event notequals up" to catch all fail states, unless you really want separate checkers/contacts depending on what's wrong with the thing :)
On 2016-02-08 15:05, Moerman, Maarten wrote:
You can alert when the value does not equal 2 (from the looks of it)
Maarten
Maarten Moerman | Mgr, Network Engineering | eBay Classifieds | +31-655122247 | mmoerman@ebay.com
From: observium on behalf of Spencer Ryan Reply-To: Observium Network Observation System Date: Monday, February 8, 2016 at 3:03 PM To: Observium Network Observation System Subject: [Observium] Alert check config for a UPS "Status" entry
We'd like to alert when any of our APC UPS'es output status is not "online"
I see an alert check type is "status" but I'm not sure what to use for the other settings.
Right now we have a UPS in hardware bypass due to a bad inverter (ugh) and the status entry says "event alert, status hardwareFailureBypass".
Any tips?
- Spencer Ryan* | Senior Systems Administrator | sryan@arbor.net
sryan@arbor.net *Arbor Networks* +1.734.794.5033 (d) | +1.734.846.2053 (m) http://www.arbornetworks.com/www.arbornetworks.com
observium mailing listobservium@observium.orghttp://postman.memetic.org/cgi-bin/mailman/listinfo/observium
observium mailing list observium@observium.org http://postman.memetic.org/cgi-bin/mailman/listinfo/observium
participants (3)
-
Moerman, Maarten
-
Spencer Ryan
-
Tom Laermans