I've asked about this before but how hard would it be for you guys to implement alert dependencies?
The easiest way I can think of doing it would be to simply let us set a "parent" device for anything, and if that device is offline don't send any alerts for downstream devices.
For example we have a testlab that has no UPS/Generator power that we monitor about 200 devices, when the building loses power we get those 200 alarms about devices being offline, when in reality there is a single 6500 as the gateway, and if that switch is offline, i know the rest will be.
We don't want to disable the offline alarms because we do want to know when individual devices drop out.
Thanks!
*Spencer Ryan* | Senior Systems Administrator | sryan@arbor.net *Arbor Networks* +1.734.794.5033 (d) | +1.734.846.2053 (m) www.arbornetworks.com

This is fiddly due to the way our poller runs as separated processes. You'd not be able to reliably suppress alerts this way, without also delaying them by up to 5 minutes.
Adam.
Sent from BlueMail
On 20 May 2016, 19:07, at 19:07, Spencer Ryan sryan@arbor.net wrote:
I've asked about this before but how hard would it be for you guys to implement alert dependencies?
The easiest way I can think of doing it would be to simply let us set a "parent" device for anything, and if that device is offline don't send any alerts for downstream devices.
For example we have a testlab that has no UPS/Generator power that we monitor about 200 devices, when the building loses power we get those 200 alarms about devices being offline, when in reality there is a single 6500 as the gateway, and if that switch is offline, i know the rest will be.
We don't want to disable the offline alarms because we do want to know when individual devices drop out.
Thanks!
*Spencer Ryan* | Senior Systems Administrator | sryan@arbor.net *Arbor Networks* +1.734.794.5033 (d) | +1.734.846.2053 (m) www.arbornetworks.com
observium mailing list observium@observium.org http://postman.memetic.org/cgi-bin/mailman/listinfo/observium

.. or instilling intelligence into the poller to run polls based on "top level" (least amount of parent devices in tree) ... which is not impossible but definitely fiddly :-)
On 20/05/2016 21:42, Adam Armstrong wrote:
This is fiddly due to the way our poller runs as separated processes. You'd not be able to reliably suppress alerts this way, without also delaying them by up to 5 minutes.
Adam.
Sent from BlueMail http://www.bluemail.me/r
On 20 May 2016, at 19:07, Spencer Ryan <sryan@arbor.net mailto:sryan@arbor.net> wrote:
I've asked about this before but how hard would it be for you guys to implement alert dependencies? The easiest way I can think of doing it would be to simply let us set a "parent" device for anything, and if that device is offline don't send any alerts for downstream devices. For example we have a testlab that has no UPS/Generator power that we monitor about 200 devices, when the building loses power we get those 200 alarms about devices being offline, when in reality there is a single 6500 as the gateway, and if that switch is offline, i know the rest will be. We don't want to disable the offline alarms because we do want to know when individual devices drop out. Thanks! * Spencer Ryan* | Senior Systems Administrator | sryan@arbor.net <mailto:sryan@arbor.net> *Arbor Networks* +1.734.794.5033 (d) | +1.734.846.2053 (m) www.arbornetworks.com <http://www.arbornetworks.com/> ------------------------------------------------------------------------ observium mailing list observium@observium.org http://postman.memetic.org/cgi-bin/mailman/listinfo/observium
observium mailing list observium@observium.org http://postman.memetic.org/cgi-bin/mailman/listinfo/observium

Do the alerts get generated as each device polls? Just run the alerter when all pollers complete and take the parent device into account? On May 20, 2016 3:44 PM, "Tom Laermans" tom.laermans@powersource.cx wrote:
.. or instilling intelligence into the poller to run polls based on "top level" (least amount of parent devices in tree) ... which is not impossible but definitely fiddly :-)
On 20/05/2016 21:42, Adam Armstrong wrote:
This is fiddly due to the way our poller runs as separated processes. You'd not be able to reliably suppress alerts this way, without also delaying them by up to 5 minutes.
Adam.
Sent from BlueMail http://www.bluemail.me/r
On 20 May 2016, at 19:07, Spencer Ryan sryan@arbor.net wrote:
I've asked about this before but how hard would it be for you guys to implement alert dependencies?
The easiest way I can think of doing it would be to simply let us set a "parent" device for anything, and if that device is offline don't send any alerts for downstream devices.
For example we have a testlab that has no UPS/Generator power that we monitor about 200 devices, when the building loses power we get those 200 alarms about devices being offline, when in reality there is a single 6500 as the gateway, and if that switch is offline, i know the rest will be.
We don't want to disable the offline alarms because we do want to know when individual devices drop out.
Thanks!
- Spencer Ryan* | Senior Systems Administrator | sryan@arbor.net
*Arbor Networks* +1.734.794.5033 (d) | +1.734.846.2053 (m) www.arbornetworks.com
observium mailing listobservium@observium.orghttp://postman.memetic.org/cgi-bin/mailman/listinfo/observium
observium mailing listobservium@observium.orghttp://postman.memetic.org/cgi-bin/mailman/listinfo/observium
observium mailing list observium@observium.org http://postman.memetic.org/cgi-bin/mailman/listinfo/observium

What, and delay alerts by a possible 5 minutes?
I know many if our users would hunt you down and stab you in the face for making such a suggestion.
And his do you know that the upstream device which was up at the start of the poller run is still up at the end?
Messing with poller order is a bad idea.
Adam.
Sent from BlueMail
On 20 May 2016, 20:48, at 20:48, Spencer Ryan sryan@arbor.net wrote:
Do the alerts get generated as each device polls? Just run the alerter when all pollers complete and take the parent device into account? On May 20, 2016 3:44 PM, "Tom Laermans" tom.laermans@powersource.cx wrote:
.. or instilling intelligence into the poller to run polls based on
"top
level" (least amount of parent devices in tree) ... which is not
impossible
but definitely fiddly :-)
On 20/05/2016 21:42, Adam Armstrong wrote:
This is fiddly due to the way our poller runs as separated processes. You'd not be able to reliably suppress alerts this way, without also delaying them by up to 5 minutes.
Adam.
Sent from BlueMail http://www.bluemail.me/r
On 20 May 2016, at 19:07, Spencer Ryan sryan@arbor.net wrote:
I've asked about this before but how hard would it be for you guys
to
implement alert dependencies?
The easiest way I can think of doing it would be to simply let us
set a
"parent" device for anything, and if that device is offline don't
send any
alerts for downstream devices.
For example we have a testlab that has no UPS/Generator power that
we
monitor about 200 devices, when the building loses power we get
those 200
alarms about devices being offline, when in reality there is a
single 6500
as the gateway, and if that switch is offline, i know the rest will
be.
We don't want to disable the offline alarms because we do want to
know
when individual devices drop out.
Thanks!
- Spencer Ryan* | Senior Systems Administrator | sryan@arbor.net
*Arbor Networks* +1.734.794.5033 (d) | +1.734.846.2053 (m) www.arbornetworks.com
observium mailing
listobservium@observium.orghttp://postman.memetic.org/cgi-bin/mailman/listinfo/observium
observium mailing
listobservium@observium.orghttp://postman.memetic.org/cgi-bin/mailman/listinfo/observium
observium mailing list observium@observium.org http://postman.memetic.org/cgi-bin/mailman/listinfo/observium
observium mailing list observium@observium.org http://postman.memetic.org/cgi-bin/mailman/listinfo/observium

Just like everything with the poller it would be a consistent 5 minutes.
I think more of my colleagues here would trade a slight delay in alerting for not getting tens/hundreds of alerts when a site drops offline.
You don't need to get fancy, if the device was offline when it was polled, treat it offline for that cycle. If it's up, it's up.
*Spencer Ryan* | Senior Systems Administrator | sryan@arbor.net *Arbor Networks* +1.734.794.5033 (d) | +1.734.846.2053 (m) www.arbornetworks.com
On Fri, May 20, 2016 at 5:48 PM, Adam Armstrong adama@memetic.org wrote:
What, and delay alerts by a possible 5 minutes?
I know many if our users would hunt you down and stab you in the face for making such a suggestion.
And his do you know that the upstream device which was up at the start of the poller run is still up at the end?
Messing with poller order is a bad idea.
Adam.
Sent from BlueMail http://www.bluemail.me/r
On 20 May 2016, at 20:48, Spencer Ryan sryan@arbor.net wrote:
Do the alerts get generated as each device polls? Just run the alerter when all pollers complete and take the parent device into account? On May 20, 2016 3:44 PM, "Tom Laermans" tom.laermans@powersource.cx wrote:
.. or instilling intelligence into the poller to run polls based on "top level" (least amount of parent devices in tree) ... which is not impossible but definitely fiddly :-)
On 20/05/2016 21:42, Adam Armstrong wrote:
This is fiddly due to the way our poller runs as separated processes. You'd not be able to reliably suppress alerts this way, without also delaying them by up to 5 minutes.
Adam.
Sent from BlueMail http://www.bluemail.me/r
On 20 May 2016, at 19:07, Spencer Ryan sryan@arbor.net wrote:
I've asked about this before but how hard would it be for you guys to implement alert dependencies?
The easiest way I can think of doing it would be to simply let us set a "parent" device for anything, and if that device is offline don't send any alerts for downstream devices.
For example we have a testlab that has no UPS/Generator power that we monitor about 200 devices, when the building loses power we get those 200 alarms about devices being offline, when in reality there is a single 6500 as the gateway, and if that switch is offline, i know the rest will be.
We don't want to disable the offline alarms because we do want to know when individual devices drop out.
Thanks!
- Spencer Ryan* | Senior Systems Administrator | sryan@arbor.net
sryan@arbor.net *Arbor Networks* +1.734.794.5033 (d) | +1.734.846.2053 (m) http://www.arbornetworks.com/www.arbornetworks.com
observium mailing listobservium@observium.orghttp://postman.memetic.org/cgi-bin/mailman/listinfo/observium
observium mailing listobservium@observium.orghttp://postman.memetic.org/cgi-bin/mailman/listinfo/observium
observium mailing list observium@observium.org http://postman.memetic.org/cgi-bin/mailman/listinfo/observium
observium mailing list observium@observium.org http://postman.memetic.org/cgi-bin/mailman/listinfo/observium
observium mailing list observium@observium.org http://postman.memetic.org/cgi-bin/mailman/listinfo/observium

Having the alert code say "Was device X online?" if false ->stop is bullshit magic?
Pretty much any other monitoring platform has the ability for parent/child relationships.
*Spencer Ryan* | Senior Systems Administrator | sryan@arbor.net *Arbor Networks* +1.734.794.5033 (d) | +1.734.846.2053 (m) www.arbornetworks.com
On Fri, May 20, 2016 at 5:51 PM, Spencer Ryan sryan@arbor.net wrote:
Just like everything with the poller it would be a consistent 5 minutes.
I think more of my colleagues here would trade a slight delay in alerting for not getting tens/hundreds of alerts when a site drops offline.
You don't need to get fancy, if the device was offline when it was polled, treat it offline for that cycle. If it's up, it's up.
*Spencer Ryan* | Senior Systems Administrator | sryan@arbor.net *Arbor Networks* +1.734.794.5033 (d) | +1.734.846.2053 (m) www.arbornetworks.com
On Fri, May 20, 2016 at 5:48 PM, Adam Armstrong adama@memetic.org wrote:
What, and delay alerts by a possible 5 minutes?
I know many if our users would hunt you down and stab you in the face for making such a suggestion.
And his do you know that the upstream device which was up at the start of the poller run is still up at the end?
Messing with poller order is a bad idea.
Adam.
Sent from BlueMail http://www.bluemail.me/r
On 20 May 2016, at 20:48, Spencer Ryan sryan@arbor.net wrote:
Do the alerts get generated as each device polls? Just run the alerter when all pollers complete and take the parent device into account? On May 20, 2016 3:44 PM, "Tom Laermans" tom.laermans@powersource.cx wrote:
.. or instilling intelligence into the poller to run polls based on "top level" (least amount of parent devices in tree) ... which is not impossible but definitely fiddly :-)
On 20/05/2016 21:42, Adam Armstrong wrote:
This is fiddly due to the way our poller runs as separated processes. You'd not be able to reliably suppress alerts this way, without also delaying them by up to 5 minutes.
Adam.
Sent from BlueMail http://www.bluemail.me/r
On 20 May 2016, at 19:07, Spencer Ryan sryan@arbor.net wrote:
I've asked about this before but how hard would it be for you guys to implement alert dependencies?
The easiest way I can think of doing it would be to simply let us set a "parent" device for anything, and if that device is offline don't send any alerts for downstream devices.
For example we have a testlab that has no UPS/Generator power that we monitor about 200 devices, when the building loses power we get those 200 alarms about devices being offline, when in reality there is a single 6500 as the gateway, and if that switch is offline, i know the rest will be.
We don't want to disable the offline alarms because we do want to know when individual devices drop out.
Thanks!
- Spencer Ryan* | Senior Systems Administrator | sryan@arbor.net
sryan@arbor.net *Arbor Networks* +1.734.794.5033 (d) | +1.734.846.2053 (m) http://www.arbornetworks.com/www.arbornetworks.com
observium mailing listobservium@observium.orghttp://postman.memetic.org/cgi-bin/mailman/listinfo/observium
observium mailing listobservium@observium.orghttp://postman.memetic.org/cgi-bin/mailman/listinfo/observium
observium mailing list observium@observium.org http://postman.memetic.org/cgi-bin/mailman/listinfo/observium
observium mailing list observium@observium.org http://postman.memetic.org/cgi-bin/mailman/listinfo/observium
observium mailing list observium@observium.org http://postman.memetic.org/cgi-bin/mailman/listinfo/observium

Yes, because it will probably cause confusing behaviour.
Adam.
Sent from BlueMail
On 20 May 2016, 22:53, at 22:53, Spencer Ryan sryan@arbor.net wrote:
Having the alert code say "Was device X online?" if false ->stop is bullshit magic?
Pretty much any other monitoring platform has the ability for parent/child relationships.
*Spencer Ryan* | Senior Systems Administrator | sryan@arbor.net *Arbor Networks* +1.734.794.5033 (d) | +1.734.846.2053 (m) www.arbornetworks.com
On Fri, May 20, 2016 at 5:51 PM, Spencer Ryan sryan@arbor.net wrote:
Just like everything with the poller it would be a consistent 5
minutes.
I think more of my colleagues here would trade a slight delay in
alerting
for not getting tens/hundreds of alerts when a site drops offline.
You don't need to get fancy, if the device was offline when it was
polled,
treat it offline for that cycle. If it's up, it's up.
*Spencer Ryan* | Senior Systems Administrator | sryan@arbor.net *Arbor Networks* +1.734.794.5033 (d) | +1.734.846.2053 (m) www.arbornetworks.com
On Fri, May 20, 2016 at 5:48 PM, Adam Armstrong adama@memetic.org
wrote:
What, and delay alerts by a possible 5 minutes?
I know many if our users would hunt you down and stab you in the
face for
making such a suggestion.
And his do you know that the upstream device which was up at the
start of
the poller run is still up at the end?
Messing with poller order is a bad idea.
Adam.
Sent from BlueMail http://www.bluemail.me/r
On 20 May 2016, at 20:48, Spencer Ryan sryan@arbor.net wrote:
Do the alerts get generated as each device polls? Just run the
alerter
when all pollers complete and take the parent device into account? On May 20, 2016 3:44 PM, "Tom Laermans"
wrote:
.. or instilling intelligence into the poller to run polls based
on
"top level" (least amount of parent devices in tree) ... which is
not
impossible but definitely fiddly :-)
On 20/05/2016 21:42, Adam Armstrong wrote:
This is fiddly due to the way our poller runs as separated
processes.
You'd not be able to reliably suppress alerts this way, without
also
delaying them by up to 5 minutes.
Adam.
Sent from BlueMail http://www.bluemail.me/r
On 20 May 2016, at 19:07, Spencer Ryan sryan@arbor.net wrote:
I've asked about this before but how hard would it be for you
guys to
implement alert dependencies?
The easiest way I can think of doing it would be to simply let us
set
a "parent" device for anything, and if that device is offline
don't send
any alerts for downstream devices.
For example we have a testlab that has no UPS/Generator power
that we
monitor about 200 devices, when the building loses power we get
those 200
alarms about devices being offline, when in reality there is a
single 6500
as the gateway, and if that switch is offline, i know the rest
will be.
We don't want to disable the offline alarms because we do want to
know
when individual devices drop out.
Thanks!
- Spencer Ryan* | Senior Systems Administrator |
sryan@arbor.net *Arbor Networks* +1.734.794.5033 (d) | +1.734.846.2053 (m) http://www.arbornetworks.com/www.arbornetworks.com
observium mailing
listobservium@observium.orghttp://postman.memetic.org/cgi-bin/mailman/listinfo/observium
observium mailing
listobservium@observium.orghttp://postman.memetic.org/cgi-bin/mailman/listinfo/observium
observium mailing list observium@observium.org http://postman.memetic.org/cgi-bin/mailman/listinfo/observium
observium mailing list observium@observium.org http://postman.memetic.org/cgi-bin/mailman/listinfo/observium
observium mailing list observium@observium.org http://postman.memetic.org/cgi-bin/mailman/listinfo/observium
observium mailing list observium@observium.org http://postman.memetic.org/cgi-bin/mailman/listinfo/observium

You still would have unexpected behaviour. I think in this case, it is preferred to have expected behaviour rather than doing bullshit magic and voodoo in the background.
Adam.
Sent from BlueMail
On 20 May 2016, 20:44, at 20:44, Tom Laermans tom.laermans@powersource.cx wrote:
.. or instilling intelligence into the poller to run polls based on "top level" (least amount of parent devices in tree) ... which is not impossible but definitely fiddly :-)
On 20/05/2016 21:42, Adam Armstrong wrote:
This is fiddly due to the way our poller runs as separated processes.
You'd not be able to reliably suppress alerts this way, without also delaying them by up to 5 minutes.
Adam.
Sent from BlueMail http://www.bluemail.me/r
On 20 May 2016, at 19:07, Spencer Ryan <sryan@arbor.net mailto:sryan@arbor.net> wrote:
I've asked about this before but how hard would it be for you
guys
to implement alert dependencies? The easiest way I can think of doing it would be to simply let us set a "parent" device for anything, and if that device is offline don't send any alerts for downstream devices. For example we have a testlab that has no UPS/Generator power
that
we monitor about 200 devices, when the building loses power we
get
those 200 alarms about devices being offline, when in reality there is a single 6500 as the gateway, and if that switch is offline, i know the rest will be. We don't want to disable the offline alarms because we do want to know when individual devices drop out. Thanks! * Spencer Ryan* | Senior Systems Administrator | sryan@arbor.net <mailto:sryan@arbor.net> *Arbor Networks* +1.734.794.5033 (d) | +1.734.846.2053 (m) www.arbornetworks.com <http://www.arbornetworks.com/>
observium mailing list observium@observium.org http://postman.memetic.org/cgi-bin/mailman/listinfo/observium
observium mailing list observium@observium.org http://postman.memetic.org/cgi-bin/mailman/listinfo/observium