Hy observium-users,
we're using observium with many devices and all sensors report a correct state. But with Mikrotik RB2011 we're getting temperature and voltage warnings from "System 0". The reported values seem ok, but the thresholds are wrong. e.g. temperature 0C - 5.6C, voltage 1.04V - 1.4V
how can we fix this behaviour?
screens attached: [cid:image001.png@01CF75D6.499A3DD0] [cid:image002.png@01CF75D6.499A3DD0]
Thx,
Ing. Christian Mladek
hotze.com GmbH A-6020 Innsbruck, Eduard-Bodem-Gasse 6 Telefon: +43 512 353640-0 Fax: +43 512 353640-50 Support: DW 910 Verkauf: DW 920 Buchhaltung: DW 930 Informationen gem. UGB: FB Nr. 287217d, LG Innsbruck, vgl. http://impressum.hotze.com/ Sämtliche Leistungen werden ausschliesslich auf Grundlage unserer AGB erbracht, diese können Sie hier nachlesen: http://www.hotze.com/ueber_uns/agb/
Hi,
you can go into the settings in the device on Observium and set custom values…
this is what i had to do with our Mikrotik switches i monitor
Devices -> select device -> Settings Icon -> Sensors
Then set your High and Low values here Also make sure Custom Limits is set to YES
then save :-)
Hope this helps
Regards
Simon
On 22 May 2014, at 14:55, Christian Mladek c.mladek@hotze.com wrote:
Hy observium-users,
we’re using observium with many devices and all sensors report a correct state. But with Mikrotik RB2011 we’re getting temperature and voltage warnings from „System 0“. The reported values seem ok, but the thresholds are wrong. e.g. temperature 0C – 5.6C, voltage 1.04V – 1.4V
how can we fix this behaviour?
screens attached: <image001.png> <image002.png>
Thx,
Ing. Christian Mladek
hotze.com GmbH A-6020 Innsbruck, Eduard-Bodem-Gasse 6 Telefon: +43 512 353640-0 Fax: +43 512 353640-50 Support: DW 910 Verkauf: DW 920 Buchhaltung: DW 930 Informationen gem. UGB: FB Nr. 287217d, LG Innsbruck, vgl. http://impressum.hotze.com/ Sämtliche Leistungen werden ausschliesslich auf Grundlage unserer AGB erbracht, diese können Sie hier nachlesen: http://www.hotze.com/ueber_uns/agb/
observium mailing list observium@observium.org http://postman.memetic.org/cgi-bin/mailman/listinfo/observium
Hi,
thx, this worked!
Regards, Christian
Von: observium [mailto:observium-bounces@observium.org] Im Auftrag von Simon Smith Gesendet: Donnerstag, 22. Mai 2014 16:00 An: Observium Network Observation System Betreff: Re: [Observium] Mikrotik RouterOS 6 Sensors
Hi,
you can go into the settings in the device on Observium and set custom values...
this is what i had to do with our Mikrotik switches i monitor
Devices -> select device -> Settings Icon -> Sensors
Then set your High and Low values here Also make sure Custom Limits is set to YES
then save :-)
Hope this helps
Regards
Simon
On 22 May 2014, at 14:55, Christian Mladek <c.mladek@hotze.commailto:c.mladek@hotze.com> wrote:
Hy observium-users,
we're using observium with many devices and all sensors report a correct state. But with Mikrotik RB2011 we're getting temperature and voltage warnings from "System 0". The reported values seem ok, but the thresholds are wrong. e.g. temperature 0C - 5.6C, voltage 1.04V - 1.4V
how can we fix this behaviour?
screens attached: <image001.png> <image002.png>
Thx,
Ing. Christian Mladek
hotze.comhttp://hotze.com/ GmbH A-6020 Innsbruck, Eduard-Bodem-Gasse 6 Telefon: +43 512 353640-0 Fax: +43 512 353640-50 Support: DW 910 Verkauf: DW 920 Buchhaltung: DW 930 Informationen gem. UGB: FB Nr. 287217d, LG Innsbruck, vgl. http://impressum.hotze.com/ Sämtliche Leistungen werden ausschliesslich auf Grundlage unserer AGB erbracht, diese können Sie hier nachlesen: http://www.hotze.com/ueber_uns/agb/
_______________________________________________ observium mailing list observium@observium.orgmailto:observium@observium.org http://postman.memetic.org/cgi-bin/mailman/listinfo/observium
participants (2)
-
Christian Mladek
-
Simon Smith