Hello all,
I have the fallowing UPS's With APC 9617 Management cards
Smart-UPS 1000 600.3.D Does not report Current draw Smart-UPS RT 2000 XL 801.3.D Everything works SMART-UPS 2200 80.11.D Does not report Current draw
Everything else is reporting just not the draw on the other UPS's I have updated to
APC Management Module AOS v3.7.3 / App v3.7.2
Can I Upgrade the Firmware on the UPS its self?
Still Only the 2000 XL reports Current
If I could ask it would be nice to see the Runtime on the UPS. Any sugestions on how to fix the current for the 1000 & 2200 UPS's I know there older UPS's but they work very well and was looking at getting more 1000's down the road but if I have to go with a newer UPS to get this to work that's ok to.
Thanks,
Mike
Hi Mike,
On 26/12/2012 20:08, Michael F. Kisser wrote:
Smart-UPS 1000 600.3.D Does not report Current draw
Smart-UPS RT 2000 XL 801.3.D Everything works
SMART-UPS 2200 80.11.D Does not report Current draw
Does the UPS web interface, or other monitoring systems, show current draw? It is entirely possible the UPS simply does not measure this and as such has no sensor value for it.
As far as I know, we detect and graph all possible APC SNMP OIDs.
Can I Upgrade the Firmware on the UPS its self?
You can, but we can't be sure that'll resolve your issue; see above.
Regarding the runtime and battery percentage etc, someone on IRC wanted to do this, as do I, but we haven't had time to do it yet.
Tom